    I have a client that has spec't RGB light fixtures recessed in a 24"x24" drop tile ceiling.
    These fixtures have disconnecting power cords that come with the fixtures.
    Power-con to nema 5-15 plug. He is planing on the electrical contractor to install duplex receptacles above each fixture to plug them into.
    Everything I am reading in the code says this is not approved.
    Your thoughts are appreciated.
  2. #2
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    34,438
    Mentioned
    4 Post(s)
    Tagged
    0 Thread(s)
    You are correct that cord and plug is not allowed in a dropped ceiling. Section 400.12
    400.12 Uses Not Permitted. Unless specifically permitted in
    400.10, flexible cables, flexible cord sets, and power supply
    cords shall not be used for the following:
    (1) As a substitute for the fixed wiring of a structure
    (2) Where run through holes in walls, structural ceilings,
    suspended ceilings, dropped ceilings, or floors
    (3) Where run through doorways, windows, or similar openings
    (4) Where attached to building surfaces
    Exception to (4): Flexible cord and flexible cable shall be permitted to be
    attached to building surfaces in accordance with 368.56(B) .
    (5) Where concealed by walls, floors, or ceilings or located
    above suspended or dropped ceilings
    Exception to (5): Flexible cord and flexible cable shall be permitted if
    contained within an enclosure for use in Other Spaces Used for Environmental
    Air as permitted by 300.22(C)(3).
    (6) Where installed in raceways, except as otherwise permitted
    in this Code
    (7) Where subject to physical damage