    Quote Originally Posted by rt66electric View Post
    Wouldn't be easier to add another light fixture??
    "Electricity is really just organized lightning." George Carlin
    Derek
  2. #22
    Join Date
    Oct 2018
    Las Vegas, NV
    Posts
    7
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Sure would, just no space. Cheers
  3. #23
    Join Date
    May 2005
    Richmond, Virginia
    Posts
    25,418
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    How about a fixture with two separate ballasts?
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA
  4. #24
    Join Date
    Oct 2018
    Las Vegas, NV
    Posts
    7
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Some clarification after some research
    Quote Originally Posted by petersonra View Post
    I think this chain of logic precludes doing this.
    However, I suspect you could buy a device that is not a whole lot more than a contactor to accomplish the same thing as long as it is listed properly.
    After researching this, I've realized that what we are actually accomplishing here is an emergency bypass, not a transfer. The actual transfer to emergency power happens way upstream. What we are doing is bypassing wall switches to make sure that the allocated emergency fixtures come on.
    This would not be an issue in most environments, as the fixtures designated as emergency lights in an area (e.g., a warehouse floor) would not go out when the wall switch is turned off at the end of the day. Our environment (a theatre), requires that all lights go out when switched. In this case, I believe that UL924 applies -- on power loss, we're simply bypassing the wall switch and returning the fixture to emergency power.
    So, then, a better question would have been:
    For a fixture that will accept both voltages, would it be acceptable to use a UL924 certified relay as an emergency bypass, with 120 volts across the NO contacts and 277 on the NC contacts?
  5. #25
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    41,295
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by dng View Post
    To me bypass would mean you have a control in parallel with the regular control - maybe a contactor contact that is in parallel with a wall switch. You are talking about bringing entirely different source to power the same load, and likely providing some sort of isolation so it can't backfeed into the circuit from the first source. If transfer occurred upstream, then you would be "bypassing" the switch in the original circuit but still supplying with same circuit - only change is in the switching arrangements.
    I live for today, I'm just a day behind.
  6. #26
    Join Date
    Oct 2018
    Las Vegas, NV
    Posts
    7
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Answering my own question here: No. This would not be a bypass like the rest of our facility, it would be a transfer.