    Phase rotation

    Have existing panels and distribution gear being demolished. Loads are Being temped out and then swung over to new panels gear. If there a chance that there could be an issue with phase rotation of motors or elevators once connected to new panels and gear? How do you prevent this or check and fix it if it's out of phase? Thanks

    Sent from my SM-N960U using Tapatalk

  2. #2
    Join Date
    Sep 2008
    Location
    UK
    Posts
    12,239
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by mstrlucky74 View Post
    Have existing panels and distribution gear being demolished. Loads are Being temped out and then swung over to new panels gear. If there a chance that there could be an issue with phase rotation of motors or elevators once connected to new panels and gear? How do you prevent this or check and fix it if it's out of phase? Thanks

    Sent from my SM-N960U using Tapatalk
    Check the direction of rotation before you couple the motors up.
    Si hoc legere scis nimium eruditionis habes.

  3. #3
    Join Date
    Jun 2003
    Location
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    10,302
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    We would have checked phase rotation at the controllers and tagged them, BK,RD,BL or whatever before removal.
    Tom
    TBLO

  4. #4
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    26,360
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Use a phase rotation meter on the existing and then make sure that the temp has the same rotation. We use these:

    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  5. #5
    Join Date
    Sep 2012
    Location
    NJ
    Posts
    2,288
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ptonsparky View Post
    We would have checked phase rotation at the controllers and tagged them, BK,RD,BL or whatever before removal.
    How does that stop them from going out of phase? What a out motors with disconnects and no controllers?

    Sent from my SM-N960U using Tapatalk

  6. #6
    Join Date
    Sep 2012
    Location
    NJ
    Posts
    2,288
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    What the process in checking phase rotation and changing it if need be? Thanks

    Sent from my SM-N960U using Tapatalk

  7. #7
    Join Date
    Feb 2003
    Location
    Baltimore, Md.
    Posts
    135
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Read the directions. That is the easiest way. You will need a phase rotation meter and they come with the directions.

  8. #8
    Join Date
    Sep 2012
    Location
    NJ
    Posts
    2,288
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Ty

    Sent from my SM-N960U using Tapatalk

  9. #9
    Join Date
    Jun 2003
    Location
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    10,302
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    We use T+Pros that have a rotation indicator built into them.
    Read The Fine Manual is of course the best method.
    Tom
    TBLO

  10. #10
    Join Date
    Jun 2003
    Location
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    10,302
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Maybe in the perfect world ABC rotation at the SE means ABC throughout the plant all the way to the motors, but don’t count on it.