Page 2 of 2 FirstFirst 12
Results 11 to 16 of 16
Thread: Transformer X0 bonding
  1. #11
    Join Date
    Mar 2015
    nyc
    Posts
    30
    Bonded and done
    Thanks guys! I have always bonded X0 but I'm on another job & noticed no bond so before I open my mind to these guys I thought it best to reach out & verify. Thanks again!
  2. #12
    Join Date
    Apr 2015
    phoenix az
    Posts
    139
    for what its worth hood, yes, bond it but i always use a dedicated terminal block for equipments down low attached directly to the chassis, leaving the xo block with just one green bond jumper and a neutral..it also keeps that bare rebar conductor away from those ungrounded lugs... you know, when some one backs a fork lift into the tranny? oh, it happens... also is easy on the inspectors eyes B)
  3. #13
    Join Date
    Mar 2015
    nyc
    Posts
    30
    Eyes wide shut
    Quote Originally Posted by rambojoe View Post
    Yes, I agree, the AHJ always looks at a transformer so when the X0 is bonded they smile! Thanks again guys!!!
  4. #14
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    38,252
    Quote Originally Posted by Hoodood View Post
    You do realize bonding at the first disconnecting means is also an option that is code compliant?
  5. #15
    Join Date
    Apr 2015
    phoenix az
    Posts
    139
    wouldnt that mean a neutral has to be pulled with the primarys? or lines..
    we still want the separate der. neuty bonded, right?
  6. #16
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    38,252
    EGC with primary yes, neutral only if the primary winding is going to utilize it. Delta primary winding doesn't utilize a neutral conductor.
Posting Permissions