    Thanks guys! I have always bonded X0 but I'm on another job & noticed no bond so before I open my mind to these guys I thought it best to reach out & verify. Thanks again!
  2. #12
    Join Date
    Apr 2015
    phoenix az
    Posts
    262
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    for what its worth hood, yes, bond it but i always use a dedicated terminal block for equipments down low attached directly to the chassis, leaving the xo block with just one green bond jumper and a neutral..it also keeps that bare rebar conductor away from those ungrounded lugs... you know, when some one backs a fork lift into the tranny? oh, it happens... also is easy on the inspectors eyes B)
  3. #13
    Join Date
    Mar 2015
    nyc
    Posts
    30
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Eyes wide shut
    Quote Originally Posted by rambojoe View Post
    Yes, I agree, the AHJ always looks at a transformer so when the X0 is bonded they smile! Thanks again guys!!!
  4. #14
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    39,614
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Hoodood View Post
    You do realize bonding at the first disconnecting means is also an option that is code compliant?
    I live for today, I'm just a day behind.
  5. #15
    Join Date
    Apr 2015
    phoenix az
    Posts
    262
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    wouldnt that mean a neutral has to be pulled with the primarys? or lines..
    we still want the separate der. neuty bonded, right?
  6. #16
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    39,614
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    EGC with primary yes, neutral only if the primary winding is going to utilize it. Delta primary winding doesn't utilize a neutral conductor.