    Area Classification Above A Trench

    I have a situation involving a trench below a Class I Div 2 area. Per NFPA 497 it must be rated Class I Div 1. However the trench also extends beyond the boundaries of the Div 2 area above it. My understanding is that the entire trench needs the Div 1 rating. Unfortunately NFPA 497 does not address this situation. Is it possible for the area directly above a section of a Class I Div 1 trench to be nonhazardous?

  2. #2
    Join Date
    Apr 2004
    Location
    Mission Viejo, CA
    Posts
    5,238
    Quote Originally Posted by circuitrider View Post
    I have a situation involving a trench below a Class I Div 2 area. Per NFPA 497 it must be rated Class I Div 1. However the trench also extends beyond the boundaries of the Div 2 area above it. My understanding is that the entire trench needs the Div 1 rating. Unfortunately NFPA 497 does not address this situation. Is it possible for the area directly above a section of a Class I Div 1 trench to be nonhazardous?
    No. See Section 500.5(B)(2)(3). Philosophically, without an impervious barrier between them, you cannot have an unclassified location adjacent to a Division 1 location. However, the Division 2 hazard radius may be as little as 18”. It’s a judgement call.

    One of the worst fuel gas explosions occurred when a trench transported propane several miles from a source.

    This is one of the the more subtle differences between NEC Divisions (and Zones) and IEC Zones. IEC does not necessarily require a physical barrier between unclassified and Zone 1. For most practical purposes, IEC Zone 1 is a moderately upgraded NEC Division 2.
    "Bob"
    Robert B. Alexander, P.E.
    Answers based on 2014 NEC unless otherwise noted.

  3. #3
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    38,249
    Quote Originally Posted by rbalex View Post
    No. See Section 500.5(B)(2)(3). Philosophically, without an impervious barrier between them, you cannot have an unclassified location adjacent to a Division 1 location. However, the Division 2 hazard radius may be as little as 18”. It’s a judgement call.

    One of the worst fuel gas explosions occurred when a trench transported propane several miles from a source.

    This is one of the the more subtle differences between NEC Divisions (and Zones) and IEC Zones. IEC does not necessarily require a physical barrier between unclassified and Zone 1. For most practical purposes, IEC Zone 1 is a moderately upgraded NEC Division 2.
    Don't know about the incident you mentioned, but unfortunately a gas pipe in a trench doesn't trigger hazardous location if under normal operation the gas is expected to remain inside the pipe. Gas leak in an underground pipe can follow trench for a long distance though especially if soil that got filled into the trench isn't as compacted as other soil around the trench.
    I live for today, I'm just a day behind.

  4. #4
    Join Date
    Apr 2004
    Location
    Mission Viejo, CA
    Posts
    5,238
    A closed piping system in a trench (or anywhere else) does not require classification.
    "Bob"
    Robert B. Alexander, P.E.
    Answers based on 2014 NEC unless otherwise noted.

  5. #5
    Join Date
    Aug 2011
    Location
    NH
    Posts
    248
    Quote Originally Posted by rbalex View Post
    A closed piping system in a trench (or anywhere else) does not require classification.
    Not sure if you consider 'closed piping system' but some AGA standards and gas utility meter/reg station standards define 15' from flanged connections as Cl I Div 2. Although this doesn't sound like what the OP has.

  6. #6
    Join Date
    Apr 2004
    Location
    Mission Viejo, CA
    Posts
    5,238
    Quote Originally Posted by nhee2 View Post
    Not sure if you consider 'closed piping system' but some AGA standards and gas utility meter/reg station standards define 15' from flanged connections as Cl I Div 2. Although this doesn't sound like what the OP has.
    This isn’t the OP’s case. In the scenario discussed in the OP, the pressure differential between the Division 1 and unclassified locations is essentially zero and 18” is the common hazard radius.

    Closed piping has no designed route to atmosphere, such as a relief valve. Other (non-catastrophic) potential routes may be evaluated based on pressure differential, flange pressure rating, anticipated flow rates, etc. Typically, a 300psi rated flange on a 100 psi rated piping system would still be considered “closed”.
    "Bob"
    Robert B. Alexander, P.E.
    Answers based on 2014 NEC unless otherwise noted.

  7. #7
    Join Date
    Feb 2014
    Location
    Upstate SC
    Posts
    15
    Quote Originally Posted by rbalex View Post
    No. See Section 500.5(B)(2)(3). Philosophically, without an impervious barrier between them, you cannot have an unclassified location adjacent to a Division 1 location. However, the Division 2 hazard radius may be as little as 18”. It’s a judgement call.
    I believe you are right that Section 500.5(B)(2)(3) requires a Div 2 area separating Div 1 from nonhazardous. If you could justify 18" though, why not, say, 4"? Or is that what you mean by judgment call?

  8. #8
    Join Date
    Apr 2004
    Location
    Mission Viejo, CA
    Posts
    5,238
    Quote Originally Posted by circuitrider View Post
    I believe you are right that Section 500.5(B)(2)(3) requires a Div 2 area separating Div 1 from nonhazardous. If you could justify 18" though, why not, say, 4"? Or is that what you mean by judgment call?
    18" is pretty much a historic minimum. "Judgment" could put it as much as 10' although it isn't likely.
    "Bob"
    Robert B. Alexander, P.E.
    Answers based on 2014 NEC unless otherwise noted.

  9. #9
    Join Date
    Feb 2014
    Location
    Upstate SC
    Posts
    15
    Quote Originally Posted by rbalex View Post
    18" is pretty much a historic minimum. "Judgment" could put it as much as 10' although it isn't likely.
    OK, I agree. I really would like to see NFPA 497 address this though.

  10. #10
    Join Date
    Apr 2004
    Location
    Mission Viejo, CA
    Posts
    5,238
    Quote Originally Posted by circuitrider View Post
    OK, I agree. I really would like to see NFPA 497 address this though.
    NFPA 497 goes through a revision cycle just as the NEC does. Make a Public Input.
    "Bob"
    Robert B. Alexander, P.E.
    Answers based on 2014 NEC unless otherwise noted.