User Tag List
Page 1 of 2 1 2 LastLast
Results 1 to 10 of 14
Thread: Area Classification Above A Trench
  1. #1
    Join Date
    Feb 2014
    Upstate SC
    Posts
    15
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I have a situation involving a trench below a Class I Div 2 area. Per NFPA 497 it must be rated Class I Div 1. However the trench also extends beyond the boundaries of the Div 2 area above it. My understanding is that the entire trench needs the Div 1 rating. Unfortunately NFPA 497 does not address this situation. Is it possible for the area directly above a section of a Class I Div 1 trench to be nonhazardous?
  2. #2
    Join Date
    Apr 2004
    Mission Viejo, CA
    Posts
    5,542
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by circuitrider View Post
    No. See Section 500.5(B)(2)(3). Philosophically, without an impervious barrier between them, you cannot have an unclassified location adjacent to a Division 1 location. However, the Division 2 hazard radius may be as little as 18”. It’s a judgement call.
    One of the worst fuel gas explosions occurred when a trench transported propane several miles from a source.
    This is one of the the more subtle differences between NEC Divisions (and Zones) and IEC Zones. IEC does not necessarily require a physical barrier between unclassified and Zone 1. For most practical purposes, IEC Zone 1 is a moderately upgraded NEC Division 2.
    "Bob"
    Robert B. Alexander, P.E.
    Answers based on 2014 NEC unless otherwise noted.
  3. #3
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    39,120
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by rbalex View Post
    Don't know about the incident you mentioned, but unfortunately a gas pipe in a trench doesn't trigger hazardous location if under normal operation the gas is expected to remain inside the pipe. Gas leak in an underground pipe can follow trench for a long distance though especially if soil that got filled into the trench isn't as compacted as other soil around the trench.
    I live for today, I'm just a day behind.
  4. #4
    Join Date
    Apr 2004
    Mission Viejo, CA
    Posts
    5,542
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    A closed piping system in a trench (or anywhere else) does not require classification.
    "Bob"
  5. #5
    Join Date
    Feb 2014
    Upstate SC
    Posts
    15
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I believe you are right that Section 500.5(B)(2)(3) requires a Div 2 area separating Div 1 from nonhazardous. If you could justify 18" though, why not, say, 4"? Or is that what you mean by judgment call?
  6. #6
    Join Date
    Apr 2004
    Mission Viejo, CA
    Posts
    5,542
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    18" is pretty much a historic minimum. "Judgment" could put it as much as 10' although it isn't likely.
    "Bob"
  7. #7
    Join Date
    Aug 2004
    Northern illinois
    Posts
    17,045
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    A few questions just out of curiosity.
    Who has a trench that is several miles long without any breaks?
    Would an 18 inch break in the trench have done any good? Several miles of propane is a lot of propane. It seems to me that much propane would just spill over an 18 inch separation at grade.
    Bob
  8. #8
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    39,120
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by petersonra View Post
    could be propane got into some other trench for whatever reason and followed it, like underground crossing
  9. #9
    Join Date
    Apr 2004
    Mission Viejo, CA
    Posts
    5,542
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Propane is extremely heavy and can maintain an explosive mixture for a long time. As part of an API study, a slow leak with a relatively low wind a propane leak can remain explosive for at least 3 miles before it becomes dispersed.
    I won’t name the city. Basically, the trench was an above ground water drainage system that fed into a catch basin. The propane collected in the basin. How long the initial leak occurred is unknown.
    "Bob"
  10. #10
    Join Date
    Aug 2004
    Northern illinois
    Posts
    17,045
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by kwired View Post
    That would still be a long trench. Bob A. did not say a tunnel, or culvert, or pipe. He is very careful with his words.
    Bob
Posting Permissions
  • You may not post replies
  • You may not edit your posts