    Ok, since I am learning and this is one of the things I am learning, let’s see how bad I screw up..12 wire is 2.25... three gang box 44 cubic inches..lol...
    grounds...2.25
    clamps.....2.25
    three yokes..3*2.25 or 6.75
    so now left with 44-10.25=33.75 / 2.25... doing this in my head so.. 4 wires is 9 so 12 wires is 27, plus another two wires is 4.5 or 31.5 ... so can fit 7 lives and 7 neutrals into the box...
    not using MWBCs..lol...
    Student of electrical codes. Please Take others advice first.
  2. #22
    Join Date
    Feb 2003
    Minnesota
    Posts
    7,067
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Adamjamma View Post
    grounds...2.25
    clamps.....2.25
    Each yoke counts as two conductors. . .
    Another Al in Minnesota
  3. #23
    Join Date
    May 2018
    Jamaica and london
    Posts
    1,301
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Ok..two not one. Thanks. So six conductors in a three gang for yokes, one conductor for all grounds and one conductor for all clamps, then figure out how much is left to figure number of conductors
  4. #24
    Join Date
    Dec 2011
    Ocala, Florida, USA
    Posts
    3,008
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by al hildenbrand View Post
    The question, as written in the OP, does not say if the cable clamp is part of the manufactured box, or if the cable clamp is a snap in clamp in a K.O.
    Are you talking about the flap that holds a cable that is pushed in to the box? If so, I would not consider this to be a clamp per 314.16(B)(2) Now if it is a brown box with actual clamps that is different.
    I know what I don't know, and I know where to go to find it!
  5. #25
    Join Date
    Feb 2003
    Minnesota
    Posts
    7,067
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Strathead View Post
    I agree with Jumper on this one. I can't see a way to avoid a clamp fill deduction when the clamp is factory molded into the wall of the box, because of one of the two meanings of "in the box". "Internal cable clamps" are factory made "in the box."
    In the past, I've interpreted "internal" to mean inside the air volume of the box, which allows the box wall to neither be inside, or outside. But this language highlighted in red below doesn't allow me, in my opinion, to make that interpretation anymore.
    "In the box" means BOTH in the material that is the box itself, AND the air volume inside the material that the box is made of, in my opinion.
    2011 NEC 314.16(B)
    (2) Clamp Fill.
    Where one or more internal cable clamps, whether factory or field supplied, are present in the box, a single volume allowance in accordance with Table 314.16(B) shall be made based on the largest conductor present in the box. No allowance shall be required for a cable connector with its clamping mechanism outside the box.
    2017 NEC 314.16(B)
    (2) Clamp Fill.
    A clamp assembly that incorporates a cable termination for the cable conductors shall be listed and marked for use with specific nonmetallic boxes. Conductors that originate within the clamp assembly shall be included in conductor fill calculations covered in 314.16(B)(1) as though they entered from outside the box. The clamp assembly shall not require a fill allowance, but the volume of the portion of the assembly that remains within the box after installation shall be excluded from the box volume as marked 314.16(A)(2)
  6. #26
    Join Date
    Dec 2011
    Ocala, Florida, USA
    Posts
    3,008
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I don't consider those clamps.
  7. #27
    Join Date
    Feb 2003
    Minnesota
    Posts
    7,067
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    To me, if the box manufacturer describes the "flap that holds a cable that is pushed in to the box" (to quote your words) as a cable clamp, then, regardless of how badly I abuse the flap, the flap is a cable clamp.
  8. #28
    Join Date
    May 2005
    Richmond, Virginia
    Posts
    24,536
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    That would be easy enough to determine by looking at a Carlon box with the conductor allowance molded in.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA
  9. #29
    Join Date
    May 2018
    Jamaica and london
    Posts
    1,301
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    So, Mr Hildenbrand, does section 2 actually say that if you are using a non metallic box, even if you are using cable clamps inside the box, they are not counted, but they have to be designed for use in the non metallic box? Thus, only metallic boxes using internal clamps lose conductor space for the clamps now?
    At least, that is how I read that second section from the 2017 NEC...
  10. #30
    Join Date
    Feb 2003
    Minnesota
    Posts
    7,067
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    The first sentence of the second paragraph in 2017 NEC 314.16(B)(2) that begins with: "A clamp assembly that incorporates a cable termination for the cable conductors shall be listed and marked for use with specific nonmetallic boxes." I believe this is describing a new "connector fitting" that is not just a "cable clamp" because the cable conductors terminate within the connector fitting.
    The first appearance of this "second paragraph" language is in the 2014 NEC stemming from work that two Code Making Panels did crafting Code with respect to new product coming from manufacturers. I personally have not seen this new product.
    So, that second paragraph doesn't apply, in my opinion, to plain old cable clamps and their clamp fill calculation.