Page 2 of 3 FirstFirst 123 LastLast
Results 11 to 20 of 26
Thread: Service change question
  1. #11
    Join Date
    Jan 2009
    3 Hr 2 Min from Winged Horses
    Posts
    15,760
    Quote Originally Posted by MAC702 View Post
    I've never once seen Nevada Energy in Las Vegas area change the overhead wires when I did a 100A to 200A service panel upgrade.
    Ditto.
    If they are right say 95% or more most times, why would they?
    Same for trannies.
    The odds are it will okay, they know this from experience.
    "Electricity is really just organized lightning." George Carlin
    Derek
  2. #12
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    38,252
    Quote Originally Posted by jumper View Post
    Ditto.
    Same for trannies.
    I added some HVAC load to a school one time. POCO had a run of 3 inch PVC with 500 aluminum to the building and CT metering at the building. Told them what I would be adding for load, I know they took into consideration the peak demand, how many hours it may run that way, and how many hours til it would have to cool down before next peak demand cycle. They decided to replace 500 aluminum with 500 copper based on what they figured, and upgrade 75 kVA single phase transformer to a 100 kVA. This conductor ultimately supplied 800 amps worth of multiple service disconnecting means on two separate buildings. I don't recall what actual NEC load calc would have been - too long ago, but would guess maybe 500-600 amps.
  3. #13
    Join Date
    Mar 2003
    New York
    Posts
    1,331
    Quote Originally Posted by kwired View Post
    How about when you went from 100 amp single phase to 200 amp three phase
    Why they just added one new wire and one transformer!
  4. #14
    Join Date
    May 2009
    Usa
    Posts
    1,569
    Quote Originally Posted by shputnik View Post
    When changing a 100 amp to a 200 amp service does the utilities upgrade/ increase size of thier service drop conductors?
    I have often seem contractors just tie the new 200 amp conductors to the existing wires
    Electric utilities have their own set of rules they go by when it comes to them sizing their lines.
  5. #15
    Join Date
    Jan 2009
    Posts
    15,760
    Quote Originally Posted by sameguy View Post
    Open Delta.
    Derek
  6. #16
    Join Date
    Apr 2006
    Simi Valley, CA
    Posts
    8,412
    Then it probably wouldn't work since it's residential we're talking about.
    I can build anything you want if you draw a picture of it on the back of a big enough check.
    There's no substitute for hard work....but that doesn't mean I'm going to give up trying to find one.
    John Childress
    Electrical Inspector
    IAEI / CEI / C10
    Certified Electrical Inspector
  7. #17
    Join Date
    Jan 2009
    Posts
    15,760
    Quote Originally Posted by cowboyjwc View Post
    Where did OP say this was resi?
    Derek
  8. #18
    Join Date
    Oct 2007
    New Jersey
    Posts
    6,127
    Unless you tell them you are adding significant load, like instantaneous electric water heating or electric heat they assume it will have about the same demand it had before.
    When I upgraded the service at my last house, the electrician strongly encouraged me to settle for a 150 amp upgrade. The original panel was 60 amp. His opinion was that the POCO would require a larger drop for a 200 amp panel that would have involved more expense on my side at the service drop. I bowed to his experience. Since the house was relatively small, built around 1929, with oil-fired steam heat and no central air, it didn't seem the 50 amp difference was worth pursuing with any vigor.
  9. #19
    Join Date
    May 2005
    Richmond, Virginia
    Posts
    23,513
    Gadfly, our POCO doesn't charge anything for upgrades, likely because they know they'll be selling more power. Also, it sounds like 100a would have been plenty, although the labor is the same either way.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA
  10. #20
    Join Date
    Oct 2007
    New Jersey
    Posts
    6,127
    Quote Originally Posted by LarryFine View Post
    It wasn't the POCO portion of the work that was an issue. The incoming service was attached to a fascia board and nothing else. The concern was I'd have to put in a mast to keep the POCO happy. As it was, the building department forced me to put a mast in anyway when I sold the house a few years later. And, like Tim Allen, I believe more power is always better!
Posting Permissions