Page 3 of 3 FirstFirst 123
Results 21 to 27 of 27
Thread: Service change question
  1. #21
    Join Date
    Jan 2009
    3 Hr 2 Min from Winged Horses
    Posts
    15,950
    Quote Originally Posted by LarryFine View Post
    Gadfly, our POCO doesn't charge anything for upgrades, likely because they know they'll be selling more power. Also, it sounds like 100a would have been plenty, although the labor is the same either way.
    Yeah, Dominion is good about that.
    Never paid for a new overhead drop either, plus the free meter bases.
    "Electricity is really just organized lightning." George Carlin
    Derek
  2. #22
    Join Date
    Apr 2006
    Simi Valley, CA
    Posts
    8,437
    Quote Originally Posted by jumper View Post
    Where did OP say this was resi?
    Point taken, but 100 to 200 sounds pretty resi to me.
    I can build anything you want if you draw a picture of it on the back of a big enough check.
    There's no substitute for hard work....but that doesn't mean I'm going to give up trying to find one.
    John Childress
    Electrical Inspector
    IAEI / CEI / C10
    Certified Electrical Inspector
  3. #23
    Join Date
    Jan 2009
    Posts
    15,950
    Quote Originally Posted by cowboyjwc View Post
    Prolly is resi, but....
    Derek
  4. #24
    Join Date
    Mar 2003
    New York
    Posts
    1,412
    Haha, it was for his shop; bought some 3p tooling.
  5. #25
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    38,507
    If you have much for "old downtown" businesses that are still the same thing they were 40-60 years ago, you probably have some 100 and even 60 amp single phase services still in use there.
  6. #26
    Join Date
    Jul 2005
    (44.057116, -123.103394)
    Posts
    407
    Quote Originally Posted by shputnik View Post
    When changing a 100 amp to a 200 amp service does the utilities upgrade/ increase size of thier service drop conductors?
    I have often seem contractors just tie the new 200 amp conductors to the existing wires
    Overhead? Every Utility I have worked for or dealt with has a "terms of service" that requires residential customers to notify the utility if they add 5kVA or more of load or some verbiage along those lines. So they rarely care what the main breaker says unless your submitting official notice of a load increase. Interesting aside (I have brought up here before) even under the NEC Triplex is not an NEC 310.104 "insulated" conductor. That's why they keep the definition of covered around so it can be used under the NEC.
    Manufacturers supply instructions for sizing the ampacity. Most manufacturers use standard 'code words' for *plex cables and go by the Aluminum Association tables. Link to their PDF table
    Check out Table 10 (of the pdf in the link) and the "Sun wind" Column. An EE can size triplex on the 'NEC side of a project' the same way under the NEC 310.15(C).
    Around here in older resi neighborhoods with overhead power all that triplex ends up at a transformer with at best a "50" stamped on it, As in 50kVA. I have seen several houses attached to a 15kVA (As in 62.5A @ 240V). If 3 houses actually were pulling 160-200A off a 15kVA that might not last long enough for the wire to melt.
    Another consideration besides cost is smaller wire limits the available fault current which in some states is limited to 10kAIC at the service point for residential (by Public Utility/Service Commission rules).
    Cheers
  7. #27
    Join Date
    Nov 2014
    Parker CO
    Posts
    21
    in Colorado for Xcel Energy and the other 3 states they cover, #4 can handle 200Amps as overhead freer conductors. I was blown away when I did my last overhead service change and i double checked with them and they said it was completely sufficient. you can also check the "Southwire App" on your phone and plug in "Utility" not NEC and it will tell u apmacity allowable for them.
Posting Permissions
  • You may not post replies
  • You may not edit your posts