    During transformer construction, the manufacturer has a design goal for impedance. ANSI allows for some tolerance in the final result from the design goal # and I think it is 10% plus/minus.

    They would put the tested impedance value on the nameplate, but there are times when you only know the goal value, or only an estimated value (many will guess at 2% for small utility XFMRS and 5.75% for larger), so you take a worst case estimate, which would include a -10% impedance adjustment too.