(a) Any used or secondhand material, including any fitting, device, appliance, apparatus, or other equipment reinstalled for electric wiring shall comply with the following provisions:



1. All such equipment shall be in good, satisfactory and durable condition, and adequate and satisfactory for the purpose intended or used, all of the foregoing to be determined by the Department. Such equipment must also comply with all requirements of Division 4 regarding approval.



2. No used or secondhand insulated conductors shall be used for services or for circuits operating at more than 250 volts.



3. No used, reconditioned, or refurbished molded or electronic trip molded case circuit breakers. (Added by Ord. No. 182,851, Eff. 1/3/14.)

so if in the course of working on a panel board you remove a CB you are required to replace it with a new one? That is nuts.
 

Sierrasparky

Senior Member
Location
USA
Occupation
Electrician ,contractor
Ironically, one of the largest "scrap" breaker sellers in the country, Rosen's Electric, is in LA (well, Pico Rivera, close enough)...

Yeah , They are not the only ones.

Bernard and Sons
Dan Lukow

You need it they got it.

That whole thing caught PEARL by surprise.
 