Thread: 1/2" ground rods

  1. #1
    Join Date
    Nov 2007
    Location
    Livonia, Michigan
    Posts
    363
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)

    1/2" ground rods

    Since Code requires two 5/8" copper ground rods for each new service, why does the Home Depot even carry 1/2" ground rods? You'd be surprised at all non-Code compliant items that Home Depot sells. What are 1/2" rods used for if not for service grounding electrodes?

  2. #2
    Join Date
    Jan 2009
    Location
    3 Hr 2 Min from Winged Horses
    Posts
    15,950
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jeff48356 View Post
    Since Code requires two 5/8" copper ground rods for each new service, why does the Home Depot even carry 1/2" ground rods? You'd be surprised at all non-Code compliant items that Home Depot sells. What are 1/2" rods used for if not for service grounding electrodes?
    Are they listed and stamped? Reread 250.52(5)(b). Copper rods are never required.
    "Electricity is really just organized lightning." George Carlin


    Derek

  3. #3
    Join Date
    Aug 2013
    Location
    New York, NY
    Posts
    517
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jeff48356 View Post
    Since Code requires two 5/8" copper ground rods for each new service, why does the Home Depot even carry 1/2" ground rods? You'd be surprised at all non-Code compliant items that Home Depot sells. What are 1/2" rods used for if not for service grounding electrodes?
    Telco and cable grounding? Not that that's the proper way to do it, but still...



    SceneryDriver

  4. #4
    Join Date
    Jun 2003
    Location
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    10,302
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Where does it say 5/8” for rods?
    Tom
    TBLO

  5. #5
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    4,929
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    "......Shall be 5/8 in diameter, unless listed." Is the wording
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  6. #6
    Join Date
    Jan 2009
    Location
    3 Hr 2 Min from Winged Horses
    Posts
    15,950
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by SceneryDriver View Post
    Telco and cable grounding? Not that that's the proper way to do it, but still...



    SceneryDriver
    Auxiliary and communication rods are not required to meet code min standard as long as they are properly tied to GES for the building. See 800.100 and 250.54.
    "Electricity is really just organized lightning." George Carlin


    Derek

  7. #7
    Join Date
    Jan 2009
    Location
    3 Hr 2 Min from Winged Horses
    Posts
    15,950
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ptonsparky View Post
    Where does it say 5/8” for rods?
    See reference above.
    "Electricity is really just organized lightning." George Carlin


    Derek

  8. #8
    Join Date
    Jun 2003
    Location
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    10,302
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jumper View Post
    See reference above.
    I guess I’ve never seen an unlisted rod. Even the 5/8.
    Tom
    TBLO

  9. #9
    Join Date
    Jan 2009
    Location
    3 Hr 2 Min from Winged Horses
    Posts
    15,950
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ptonsparky View Post
    I guess I’ve never seen an unlisted rod. Even the 5/8.
    Never saw a telco 4’ or 6’ rod?

    https://www.solidsignal.com/pview.as...8aAp-EEALw_wcB
    "Electricity is really just organized lightning." George Carlin


    Derek

  10. #10
    Join Date
    Jun 2003
    Location
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    10,302
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jumper View Post
    Never saw a telco 4’ or 6’ rod?
    Never pulled one up to measure it.

    i did see a bundle of short ones designated for a company that sells portable lighting systems, but nothing else that I remember.
    Tom
    TBLO