Thread: Compliant or Not

  1. #11
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    33,738
    Quote Originally Posted by charlie b View Post
    Their wording is poorly written. But I think they are describing the 6' / 12' rule for receptacles in wall spaces. They are saying that a wall receptacle that is within 12 feet of a countertop receptacle does not comply with the rules. They are not saying anything about how the receptacle is powered.


    The second image does state that the far right receptacle shall not be served by the small appliance branch circuit. I agree with Ken, it would depend on what room that was in.
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  2. #12
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    33,738
    I find it interesting that one could go so far without on the wall without a receptacle. Of course, I would never do it that way but the fact is it can be done according to the NEC
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  3. #13
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    26,025
    Am I the only one that finds have 3' 11" of wall countertop space with no receptacle absolutely stupid?
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  4. #14
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    38,252
    Quote Originally Posted by infinity View Post
    Am I the only one that finds have 3' 11" of wall countertop space with no receptacle absolutely stupid?
    NO, but if you were an inspector you couldn't write a correction notice for that either based on as written 2017 NEC.

    May or may not be what was intended but it is what resulted.
    I live for today, I'm just a day behind.

  5. #15
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    26,025
    Quote Originally Posted by kwired View Post
    NO, but if you were an inspector you couldn't write a correction notice for that either based on as written 2017 NEC.

    May or may not be what was intended but it is what resulted.
    I think that you might be correct although I don't know what was intended. This is just plain dumb.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  6. #16
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    38,252
    Quote Originally Posted by Dennis Alwon View Post
    The second image does state that the far right receptacle shall not be served by the small appliance branch circuit. I agree with Ken, it would depend on what room that was in.
    It doesn't mention SABC though, but what can or can't be done does depend on what that space is. If part of kitchen, dining, breakfast room, etc. it must be on a SABC, which can also serve counter receptacles, or not - your choice. 1500 VA for each separate SABC in your feeder/service calculations though.
    I live for today, I'm just a day behind.

  7. #17
    Join Date
    Feb 2008
    Location
    Texas
    Posts
    930
    Quote Originally Posted by infinity View Post
    Am I the only one that finds have 3' 11" of wall countertop space with no receptacle absolutely stupid?
    I'm with you and Larry on this.

    I would count the 36" section of the peninsula as counter-top for receptacle spacing because it follows the plane of the wall.

  8. #18
    Join Date
    Feb 2003
    Location
    Seattle, WA
    Posts
    19,149
    Quote Originally Posted by Dennis Alwon View Post
    The second image does state that the far right receptacle shall not be served by the small appliance branch circuit.
    No it doesn't. It says that a wall receptacle must be within 12 feet of another wall receptacle, and that it can't be 12 feet away from a countertop receptacle and satisfy the 12 foot rule.

    Charles E. Beck, P.E., Seattle
    Comments based on 2017 NEC unless otherwise noted.

  9. #19
    Join Date
    Oct 2007
    Location
    New Jersey
    Posts
    6,127
    Quote Originally Posted by Chamuit View Post
    I'm with you and Larry on this.

    I would count the 36" section of the peninsula as counter-top for receptacle spacing because it follows the plane of the wall.
    You certainly can do that, but Dennis' point is you don't have to.

  10. #20
    Join Date
    Feb 2008
    Location
    Texas
    Posts
    930
    Quote Originally Posted by gadfly56 View Post
    You certainly can do that, but Dennis' point is you don't have to.
    Yep. Code is minimum - not best design.