User Tag List
Results 1 to 2 of 2
Thread: 645.18
  1. #1
    Join Date
    Jun 2007
    Posts
    784
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    645.18
    645.18 Surge Protection for Critical Operations Data Systems.
    Surge protection shall be provided for critical operations data
    systems.
    What's exact definition of Critical Operations Data Systems equipment or rooms?
    Are the IT equipment located inside telecommunication, IDF room, closets in a commercial building or
    hospital considered as Critical Operations Data Systems?
  2. #2
    Join Date
    Jun 2017
    WI, USA
    Posts
    410
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by anbm View Post
    systems.
    645.2
    Critical Operations Data System. An information technology equipment system that requires continuous operation for reasons of public safety, emergency management, national security, or business continuity.
    645.10(B) helps to provide some context
    Somewhat along the lines of COPS 708, but not necessarily full blown.
    Typ commercial building, no. Hospital, arguably yes. With the reminder that 645 is an optionally applied article...and isn’t commonly used in healthcare settings.
Posting Permissions
  • You may not post replies
  • You may not edit your posts