    I need to boost 208 vac to 240vac what KVA Transformer do I need? The fla is 17,
  2. #2
    Join Date
    Jun 2004
    Cherry Valley NY, Seattle, WA
    Posts
    5,233
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    The manufacturers have online calculators that will size the units. I'm sure you can find it with a quick google. I know square d has one.
    Ethan Brush - East West Electric. NY, WA. MA
    "You can't generalize"
  3. #3
    Join Date
    Apr 2008
    Ann Arbor, Michigan
    Posts
    7,581
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    181911-1414 EDT
    Boggsc71:
    Quite obviously the quick answer is (240-208)*17/1000 = 0.544 . Other factors might modify this.
  4. #4
    Join Date
    Oct 2018
    Posts
    2
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by gar View Post
    181911-1414 EDT
    Boggsc71:
    Thanks for the quick response.
  5. #5
    Join Date
    May 2013
    Massachusetts
    Posts
    2,450
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    181911-1414 EDT
    Boggsc71:
    I'm confused. Why are the two voltages subtracted from one another? I would think it would be 240*17/1000 = 4.08 kVA, assuming the 17 Amperes is carried on the 240V side.
  6. #6
    Join Date
    Jun 2004
    Posts
    5,233
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Carultch View Post
    With an autotransformer, you essentially only need the kva for the voltage change.
  7. #7
    Join Date
    Nov 2015
    CA, USA
    Posts
    730
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by electrofelon View Post
    That's not entirely accurate. The current through the common part of the winding is the difference between the input and output current but the current in the part of the winding that is used by only one side of the autotransformer is the full current for that side and needs to be sized for that current. In this case, the shared winding would carry 2.6A and the secondary only part of the winding would carry 17A. If the autotransformer was wound with a single size conductor it would have to be rated for 17A. Sometimes autotransformers are wound with two conductor sizes to take advantage of the reduced current in the shared winding.
  8. #8
    Join Date
    Sep 2008
    UK
    Posts
    12,703
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by pv_n00b View Post
    So what do you think the kVA should be?
  9. #9
    Join Date
    Oct 2009
    Austin, TX, USA
    Posts
    10,672
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Multiply the delta V by the current.
  10. #10
    Join Date
    Apr 2006
    Springfield, MA, USA
    Posts
    3,504
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Most commonly for buck and boost applications under 600V, the transformer used has separate primary and secondary coils. These coils are then connected in an autotransformer configuration.
    The secondary coil(s) are 12 or 16 or 24V, and often there are 2 coils which can be in series or parallel. These transformers have 600V insulation on both the primary and secondary side. In this case the transformer secondary will be rated to carry the full current needed to give the rated kVA at the secondary voltage. The secondary coil(s) will be wound with different size wire than the primary.
    The other common autotransformer is the variable autotransformer. In this case there is only a single coil, generally made with a single size wire. The kVA rating will be at full output voltage, and at low voltage output the available kVA is less than the rating.
    -Jon