    GEC for Verizon Device

    Why did Verizon request a #4 GEC that they connected to the metal enclosure of a small device that plugs into a grounded receptacle and is feed by 2 strands of fiber?

  2. #2
    Join Date
    Aug 2009
    Location
    Tacoma, Wa
    Posts
    519
    Cuz grounding will fix anything and bigger is better don'cha know
    RichB N7NEC

  3. #3
    Join Date
    Jun 2003
    Location
    Hawthorne, New York NEC: 2014
    Posts
    3,896
    Because old requirements die hard. Somewhere in their specs from 1940 Ma Bell required a #4 to bond a terminal. Ma is always right.

    -Hal

  4. #4
    Join Date
    Nov 2016
    Location
    Montgomery County, PA, USA
    Posts
    16
    Thanks I was starting to doubt myself

  5. #5
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    19,629
    Quote Originally Posted by RAKocher View Post
    Why did Verizon request a #4 GEC that they connected to the metal enclosure of a small device that plugs into a grounded receptacle and is feed by 2 strands of fiber?
    FWIW the fiber might have steel armor....

    Sent from my XT1585 using Tapatalk

  6. #6
    Join Date
    Nov 2016
    Location
    Montgomery County, PA, USA
    Posts
    16
    Quote Originally Posted by GoldDigger View Post
    FWIW the fiber might have steel armor....

    Sent from my XT1585 using Tapatalk
    The cable that enters the bldg terminates in a separate enclosure, but the device that they connected the ground to is only connected to the other by 2 fiber optic patch cables.

  7. #7
    Join Date
    Jun 2003
    Location
    Hawthorne, New York NEC: 2014
    Posts
    3,896
    GEC... connected to the metal enclosure of a small device that plugs into a grounded receptacle
    Actually I have had big problems with that practice and no longer provide a ground unless it's derived from the ground prong of the receptacle the equipment is powered from. I used to bond to building steel, cold water line, etc. until one time the equipment was destroyed because the line cord ground and the ground screw on the housing was connected together inside the equipment. There was a voltage differential of 50 volts between the receptacle ground prong and (in this case) the building steel that I bonded the ground wire to. The connection between the line cord ground and case within the equipment was actually via a circuit board trace. The trace was vaporized destroying other components on the board in the process. The line cord was actually warm which tipped me off to what was going on.

    So I don't care what any manufacturer says, it gets grounded to the receptacle ground if it has a line cord or no ground at all. Let the line cord handle it.

    -Hal

  8. #8
    Join Date
    Nov 2016
    Location
    Montgomery County, PA, USA
    Posts
    16
    Quote Originally Posted by hbiss View Post
    Actually I have had big problems with that practice and no longer provide a ground unless it's derived from the ground prong of the receptacle the equipment is powered from. I used to bond to building steel, cold water line, etc. until one time the equipment was destroyed because the line cord ground and the ground screw on the housing was connected together inside the equipment. There was a voltage differential of 50 volts between the receptacle ground prong and (in this case) the building steel that I bonded the ground wire to. The connection between the line cord ground and case within the equipment was actually via a circuit board trace. The trace was vaporized destroying other components on the board in the process. The line cord was actually warm which tipped me off to what was going on.

    So I don't care what any manufacturer says, it gets grounded to the receptacle ground if it has a line cord or no ground at all. Let the line cord handle it.

    -Hal
    Because I did a search of the Forum for "Verizon grounds" before I posted, I did read this already and out of curiosity I did measure the resistance between the GEC that I provided and the ground at the receptacle that the device is plugged into (I did pull the plug 1st) and got 0.3 ohms. Then I touched the meter's probes together and still got 0.3 ohms. After I scraped the the probes together, it dropped to 0.1 ohm.

  9. #9
    Join Date
    Jun 2003
    Location
    Hawthorne, New York NEC: 2014
    Posts
    3,896
    Quote Originally Posted by RAKocher View Post
    Because I did a search of the Forum for "Verizon grounds" before I posted, I did read this already and out of curiosity I did measure the resistance between the GEC that I provided and the ground at the receptacle that the device is plugged into (I did pull the plug 1st) and got 0.3 ohms. Then I touched the meter's probes together and still got 0.3 ohms. After I scraped the the probes together, it dropped to 0.1 ohm.
    You don't say what the GEC is connected to but I would consider 0.1-0.3 ohms totally acceptable and as you found outside the capability of your meter to measure low resistance.

    In the situation I mentioned, it wasn't resistance but 50 volts at a considerable amount of current between the building steel and the receptacle grounding conductor making it impossible to measure the resistance and a moot point anyway. The procedure when measuring resistance should always be to first check for voltage because if there is voltage present, at the least you will get an erroneous resistance reading and at the worst you will damage your meter. So unless you are measuring the resistance of an item sitting in front of you with no chance that there could be any voltage present, check for voltage (both AC and DC) first!

    -Hal

  10. #10
    Join Date
    Nov 2016
    Location
    Montgomery County, PA, USA
    Posts
    16
    Quote Originally Posted by hbiss View Post
    You don't say what the GEC is connected to but I would consider 0.1-0.3 ohms totally acceptable and as you found outside the capability of your meter to measure low resistance.

    In the situation I mentioned, it wasn't resistance but 50 volts at a considerable amount of current between the building steel and the receptacle grounding conductor making it impossible to measure the resistance and a moot point anyway. The procedure when measuring resistance should always be to first check for voltage because if there is voltage present, at the least you will get an erroneous resistance reading and at the worst you will damage your meter. So unless you are measuring the resistance of an item sitting in front of you with no chance that there could be any voltage present, check for voltage (both AC and DC) first!

    -Hal
    I connected the GEC to a lug that's bolted to a bar-joist that's about 15' directly above the equipment board.
    When I get back there someday I'll measure for voltage. I say 'when' because I noticed they plugged into a regular receptacle instead of one of the emergency receptacles that I installed on the other side of the room a few months ago for computer equipment that I'm sure this fiber will be involved with.