User Tag List
Results 1 to 4 of 4
Thread: Power logger
  1. #1
    Join Date
    Jan 2018
    MD
    Posts
    17
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Power logger
    I was asked to determine if there is sufficient capacity to add a 200 amp 3 phase load to an existing 1200 amp 3 phase 480 volt MDP.
    I hooked up a fluke power logger to the MDP to record the power for 30 days.
    I am cretin that I connected the voltage and amperage leads correctly.
    however the reading I was getting seems odd.
    A and C phase were only pulling about 6 to 8 amps. however B phase was pulling over 160 amps. this MDP powers multiple transformers that step power down to 120/208 volt lighting and appliance panels.
    I am not surprised the 3 phases are not balanced, however I do not understand how just one phase could be so much higher than the others... everything in the MDP is 3 phase. I did not note and heavy single pole appliances in the 208 V panels.
    Just want to make sure a reading like this is possible and I did not goof something up when connecting the leads of the power logger.
  2. #2
    Join Date
    Oct 2013
    newburgh,ny
    Posts
    471
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Something don't add up
    I would think just core losses on the xformers would be more than 6-8 amps even if the phases were unloaded.
  3. #3
    Join Date
    Dec 2006
    Eastern Oregon
    Posts
    3,695
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    When I hook up our logger, I wait for the logger to record a sample and verify the results with an amp clamp before leaving the premises just so I know it's working correctly.
    Did you not amp clamp the wires while connecting the logger up?
  4. #4
    Join Date
    Jun 2017
    WI, USA
    Posts
    389
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Did you put the correct CT ratios in the meter for all phases?