Basically having a debate whether or not these single pole circuit breakers are allowed to have multi circuits or not.

I will upload a link of the pictures ASAP

But basically can some single pole breakers allow multiple circuits ??

And would be nice if u could show me what section in the nec since I have to prove this guy what is right and what is wrong.


IMG_4422.jpeg
 

cowboyjwc

Moderator
Staff member
Location
Simi Valley, CA
If you are asking if you can put two wires under the lug of a breaker to feed two circuits, then the answer is yes and no. If the breaker is listed for it you may, but other wise you would have to splice the two circuits together and pigtail them to the breaker.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
Re: two wires under one lug or spliced together, technically, wouldn't they be the same circuit if they were connected to the same circuit breaker?
I think not. If they two wires serve separate loads, then they are separate circuits. If they serve the same load, then perhaps you have a parallel installation, which may or may not be allowed. Also, whatever you have for neutral wires, this would not be a MWBC.

 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
I think not. If they two wires serve separate loads, then they are separate circuits. If they serve the same load, then perhaps you have a parallel installation, which may or may not be allowed. Also, whatever you have for neutral wires, this would not be a MWBC.


A simple example of what the OP might be suggesting.

A breaker supplies two receptacles. The receptacles are in the same room as the panel board, but on opposite sides of the CB, so the electrician ran one wire from the CB to one receptacle and a second wire from the same CB to the other receptacle.

How is this functionally any different than running a single wire from the Cb to the first receptacle and than on to the second receptacle?

You seem to be claiming there are 2 circuits in the first example and just one in the second.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
You seem to be claiming there are 2 circuits in the first example and just one in the second.
Yes I am.
How is this functionally any different than running a single wire from the Cb to the first receptacle and than on to the second receptacle?
It is functionally different in two ways.

  • First, a single wire from the CB to the first receptacle and then to the second receptacle is a series circuit. Thus, 100% the current that flows to whatever is plugged into the second receptacle will first flow through the wire leading from the CB to the first receptacle. In the other installation, the two receptacles are not in series, and they are not in parallel. The current flowing through one receptacle will not have also passed through the wire serving the other receptacle.
  • Secondly, and this is essentially the same thing said a different way, if the two wires leave the CB and head in different directions, you could completely disconnect one without reconnecting anything (i.e., just cut the wire), and not have any impact on the operation of the other. That is not possible in the series circuit configuration.

 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
Yes I am.

It is functionally different in two ways.

  • First, a single wire from the CB to the first receptacle and then to the second receptacle is a series circuit. Thus, 100% the current that flows to whatever is plugged into the second receptacle will first flow through the wire leading from the CB to the first receptacle. In the other installation, the two receptacles are not in series, and they are not in parallel. The current flowing through one receptacle will not have also passed through the wire serving the other receptacle.
  • Secondly, and this is essentially the same thing said a different way, if the two wires leave the CB and head in different directions, you could completely disconnect one without reconnecting anything (i.e., just cut the wire), and not have any impact on the operation of the other. That is not possible in the series circuit configuration.

So what if the wire goes straight down from the panel and into a j box and we bring the wires from the recpts on opposite sides of the room into it?
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
I think that following the strict NEC definition the wires are all part of one branch circuit in either case. But does being part of the same branch circuit make them one circuit? Hmmmm....
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Yes I am.

It is functionally different in two ways.

  • First, a single wire from the CB to the first receptacle and then to the second receptacle is a series circuit. Thus, 100% the current that flows to whatever is plugged into the second receptacle will first flow through the wire leading from the CB to the first receptacle. In the other installation, the two receptacles are not in series, and they are not in parallel. The current flowing through one receptacle will not have also passed through the wire serving the other receptacle.
  • Secondly, and this is essentially the same thing said a different way, if the two wires leave the CB and head in different directions, you could completely disconnect one without reconnecting anything (i.e., just cut the wire), and not have any impact on the operation of the other. That is not possible in the series circuit configuration.

In my opinion all of the conductors that receive their supply from a single OCPD are part of a single circuit.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
In my opinion all of the conductors that receive their supply from a single OCPD are part of a single circuit.
In my opinion, that opinion is not consistent with the NEC definition of "branch circuit." :happyno: You will note that that definition does not include the OCPD as being a part of the branch circuit. The branch circuit comprises the wires between the OCPD and the outlets. :happyyes:

 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
So what if the wire goes straight down from the panel and into a j box and we bring the wires from the recpts on opposite sides of the room into it?
That constitutes a combined series/parallel circuit - one circuit. In the previous discussions, we were dealing with a series circuit in one instance, and the other instance had neither a series nor a parallel configuration.

 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
In my opinion, that opinion is not consistent with the NEC definition of "branch circuit." :happyno: You will note that that definition does not include the OCPD as being a part of the branch circuit. The branch circuit comprises the wires between the OCPD and the outlets. :happyyes:

You quoted it. " ... the wires", not "the wire going in one direction and those attached to it downstream".
If there is one branch OCPD then there is one circuit downstream of it.

We could also digress into whether a single wire can be both a feeder and part of a branch circuit. And whether the U ground should be on top. :)
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
In my opinion all of the conductors that receive their supply from a single OCPD are part of a single circuit.

I agree. Would a single pole 20 amp OCPD supplying two 12/2 cables feeding kitchen counter receptacles meet the NEC requirement for a minimum of two SABC's?
 

Smart $

Esteemed Member
Location
Ohio
In my opinion all of the conductors that receive their supply from a single OCPD are part of a single circuit.

I agree. Would a single pole 20 amp OCPD supplying two 12/2 cables feeding kitchen counter receptacles meet the NEC requirement for a minimum of two SABC's?
No.

But we need to clarify Don's comment, as a 2-pole OCPD can supply either one or two branch circuits.
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Electrical Engineer - Photovoltaic Systems
Yes I am.

It is functionally different in two ways.

  • First, a single wire from the CB to the first receptacle and then to the second receptacle is a series circuit.


No, it's a parallel circuit. Loads in receptacle A are in parallel with loads in receptacle B irrespective of whether a wire set runs from A to B or if a separate wire set runs from the breaker to each receptacle.
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Electrical Engineer - Photovoltaic Systems
That constitutes a combined series/parallel circuit - one circuit. In the previous discussions, we were dealing with a series circuit in one instance, and the other instance had neither a series nor a parallel configuration.

No, it's only parallel. The configuration is different between the two ways to wire it, but it's still just a parallel circuit. None of the loads are ever in series, and without loads you don't really have a circuit.
 