    ANSI device labeling for utility

    Trying to interpret a utility line diagram revision. For a backfed AC module system they want: "Clearly label 89L disconnect , 52-IT circuit breaker"
    I have only seen ANSI Device 89-L labels on AC disconnects, but I assume it also applies to the backfed breaker.. What I can't figure out is if the branch breakers in the PV dedicated panel qualify as 52-IT and need to be labeled as such. Any thoughts? Haven't dealt much with this utility yet (ConEd).

  2. #2
    Join Date
    Sep 2004
    Location
    Vancouver, WA
    Posts
    730
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)

    89 = Switch

    Don't you love lingo. An "89" device is a switch. An "89L" would typically be a line switch but the "L" is arbitrary. I read this as they want all sources of power labeled. If you label the breaker/switch that toes to the service as "PV DISCONNECT 89L" they should be happy. As for the AC combiner, as long as there is a placard on the panel indicating it is for PV power, you should not have to label each individual switch. BUT, the POCO may have other ideas. Best to ask.
    e^(i pi) = -1

  3. #3
    Join Date
    May 2011
    Posts
    4,772
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I found this but I couldn't find anything regarding the 'IT' part of '52-IT'. I would probably assume that it doesn't matter. Well, that is, I know it doesn't matter, so I would probably label the breakers as such and see what happens.