    I have auto transformer going from supply side 208V single phase to load side 240V single phase, 5kVA. Load drawn is 16 amps by kitchen cooking appliance. On the 240V side outside of the auto transformer I have 30 amps disconnect fused at 20 amps then going to load.
    I am confused by what NEC 450.5(A) says at the end "an overcurrent device shall not be installed in series with the shunt winding of the autotransformer between Points A and B as shown in Figure 450.4(A)". So does that mean the secondary side 20 amps fused disco is not acceptable?
  2. #2
    Join Date
    Jan 2007
    Posts
    4,134
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by hhsting View Post
    The 20a fused disconnect on the secondary it fine.
    It sounds to me like you may have a Buck/Boost Transformer.
    Regardless, it's just telling you where "Not" to place an overcurrent device.
    Your overcurrent devices need to be installed on the input and output leads.
    JAP>
  3. #3
    Join Date
    Jan 2007
    Posts
    4,134
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Or possible overcurrent devices on the input only.
    JAP>
  4. #4
    Join Date
    Jan 2009
    3 Hr 2 Min from Winged Horses
    Posts
    15,966
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    You may find this ECN thread on the topic useful.
    https://www.electrical-contractor.ne...t&Number=98810