    Quote Originally Posted by Electriman View Post
    The foundation drawing shows the rebar is only 18' long and the concrete thickness is more than 2". Do I need to bond it? Do I need to bond gas pipe separately or I can assume it is bonded at the water heater?
    If the rebar is only 18' in length (seems odd) then you do not need to use a CEE. What type of gas pipe? Black pipe requires no external bonding.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  2. #12
    Join Date
    Jan 2009
    Location
    3 Hr 2 Min from Winged Horses
    Posts
    15,762
    Quote Originally Posted by infinity View Post
    If the rebar is only 18' in length (seems odd) then you do not need to use a CEE. What type of gas pipe? Black pipe requires no external bonding.
    And rebar is usually in pairs as a minimum, resi, so that would be 36’ if tied together correctly.