    That particular toggle switch does NOT have an OL heater in it. You CAN get ones that have it, but that one does not.

    All motors must have protection from overload. SOME small (typically fractional HP) motors come with built-in thermal overload protection so the control device, such as that toggle switch, do not need to provide it externally. IF the motor has thermal overload protection, it MUST state it on the nameplate, usually using the words “Thermally Protected”, or sometimes abbreviated as just “TP”, or words / abbreviations to that effect. It that is not CLEARLY designated or readable on the motor nameplate, you must assume it needs external.

    On small things like the aforementioned clock motor, it will often say it is “impedance protected”, which means it can be totally stalled and not be overloaded.
    __________________________________________________ ____________________________
    Many people are shocked when they discover I am not a good electrician...

  2. #12
    Join Date
    Sep 2012
    Location
    NJ
    Posts
    2,232
    Quote Originally Posted by Jraef View Post
    That particular toggle switch does NOT have an OL heater in it. You CAN get ones that have it, but that one does not.

    All motors must have protection from overload. SOME small (typically fractional HP) motors come with built-in thermal overload protection so the control device, such as that toggle switch, do not need to provide it externally. IF the motor has thermal overload protection, it MUST state it on the nameplate, usually using the words “Thermally Protected”, or sometimes abbreviated as just “TP”, or words / abbreviations to that effect. It that is not CLEARLY designated or readable on the motor nameplate, you must assume it needs external.

    On small things like the aforementioned clock motor, it will often say it is “impedance protected”, which means it can be totally stalled and not be overloaded.
    Thanks.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •