Thread: New Restaurant calculations help

  1. #31
    Join Date
    Oct 2007
    Posts
    1,275

    220.88 New Restaurants.

    Guy, when you use a rule, you use it as written, includint tables and notes to table. The note to Table 220.88 is as follows: "Note: Add all electrical loads, including both heating and cooling loads, to calculate the total connected load. Select the one demand factor that applies from the table, then multiply the total connected load by this single demand factor." So when you are using Section 220.88 and apply Table 220.88, we then apply note to Table 220.88. Yes, we do include a/c and heat. It doesn't have to make sense, we just have to follow the specific rule. Section 220.61 is contained in Part III of Article 220, it does not apply to any rule contained in Part IV.

  2. #32
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    33,744
    The problem is the numbers don't come out to match any of the answers given
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  3. #33
    Join Date
    Jan 2009
    Location
    3 Hr 2 Min from Winged Horses
    Posts
    15,762
    Quote Originally Posted by Dennis Alwon View Post
    The problem is the numbers don't come out to match any of the answers given
    Make one of answers 432A instead of 402A works when I ran the numbers.
    "Electricity is really just organized lightning." George Carlin


    Derek

  4. #34
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    33,744
    Quote Originally Posted by jumper View Post
    Make one of answers 432A instead of 402A works when I ran the numbers.

    That's what I had before I took out the a/c. I didn't notice the note to the table...
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  5. #35
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    33,744
    Mike agrees there is an error in the answers. The correct answer should be 441 amps based on 8000 va for lighting-- no 125% should be added to this. Add all the other stuff and you get 105,850 va

    105850/240 = 441 amps

    There is a note that he wrote that says to see annex D example D3 for continuous loads



    The answer for 26 is 656 amps
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  6. #36
    Join Date
    Jan 2009
    Location
    3 Hr 2 Min from Winged Horses
    Posts
    15,762
    Quote Originally Posted by Dennis Alwon View Post
    Mike agrees there is an error in the answers. The correct answer should be 441 amps based on 8000 va for lighting-- no 125% should be added to this. Add all the other stuff and you get 105,850 va

    105850/240 = 441 amps

    There is a note that he wrote that says to see annex D example D3 for continuous loads



    The answer for 26 is 656 amps
    Thank you. So just a minor typo. It happens.