Thread: Weird GEC found while trenching

  1. #11
    Join Date
    Jan 2009
    Location
    3 Hr 2 Min from Winged Horses
    Posts
    15,757
    Quote Originally Posted by packersparky View Post
    Yes. 250.112(M) requires the casing to be connected to the pump circuit EGC.
    Thank you.
    "Electricity is really just organized lightning." George Carlin


    Derek

  2. #12
    Join Date
    Jan 2009
    Location
    3 Hr 2 Min from Winged Horses
    Posts
    15,757
    Quote Originally Posted by ActionDave View Post


    Not quite the same ring to it as "All My Ex's Live in Texas"
    "Electricity is really just organized lightning." George Carlin


    Derek

  3. #13
    Join Date
    Apr 2007
    Location
    Huntington Beach, CA (19 Hrs. 22 Min. from Winged Horses)
    Posts
    6,709
    Quote Originally Posted by Coppersmith View Post
    LOL, I wasn't thinking about the well casing being a grounding electrode. I was thinking the well casing required grounding for some reason. I guess I don't have to worry about replacing the GEC that got sucked up into my Ditch Witch and wrapped around the axle.

    Thanks for the info.
    the ditch witch is now bonded, but needs an exothermic
    attachment to be code compliant. i'd cadweld one end to the
    auger, and the other end to the gas tank.

    this might be one of those times to invest in a electrically fired
    remote cadweld. just a thought.
    ~New signature under construction.~
    ~~~~Please excuse the mess.~~~~

  4. #14
    Join Date
    Jan 2009
    Location
    3 Hr 2 Min from Winged Horses
    Posts
    15,757
    Quote Originally Posted by Fulthrotl View Post
    the ditch witch is now bonded, but needs an exothermic
    attachment to be code compliant. i'd cadweld one end to the
    auger, and the other end to the gas tank.

    this might be one of those times to invest in a electrically fired
    remote cadweld. just a thought.
    Note to self: Never let Randy run the ditch witch. Will not get deposit back.
    "Electricity is really just organized lightning." George Carlin


    Derek

  5. #15
    Join Date
    Apr 2007
    Location
    Huntington Beach, CA (19 Hrs. 22 Min. from Winged Horses)
    Posts
    6,709
    Quote Originally Posted by jumper View Post
    Note to self: Never let Randy run the ditch witch. Will not get deposit back.
    never mind the deposit. you'll be doing good if you get the ditch witch back.

    we don't talk about what happened with the bucket wheel, and the 18" fire main.
    that's a whole 'nother story.
    ~New signature under construction.~
    ~~~~Please excuse the mess.~~~~

  6. #16
    Join Date
    Mar 2003
    Location
    Vermont
    Posts
    1,745
    One would think a mettalic well pipe , that normally makes to bedrock, would be a grand EC

    ~RJ~

  7. #17
    Join Date
    Jan 2009
    Location
    3 Hr 2 Min from Winged Horses
    Posts
    15,757
    Quote Originally Posted by Fulthrotl View Post
    never mind the deposit. you'll be doing good if you get the ditch witch back.

    we don't talk about what happened with the bucket wheel, and the 18" fire main.
    that's a whole 'nother story.
    You owe me a new key board, I laughed so hard!
    "Electricity is really just organized lightning." George Carlin


    Derek

  8. #18
    Join Date
    Dec 2011
    Location
    Wisconsin
    Posts
    460
    Quote Originally Posted by romex jockey View Post
    One would think a mettalic well pipe , that normally makes to bedrock, would be a grand EC

    ~RJ~
    I am sure most do. It can be used, just not required to be used.