    A client of mine who is a solar contractor has installed the system depicted below. His approved drawing calls for a line side tap. The inspector says this is a supply side tap. It's on the line side of the panel but the supply side of the MB. What is the correct answer?
    If that is a supply side tap, does moving the tap to the line side of the MB make it a line side tap? Note that there is already a tap ahead of it to another panel.
    He used those taps that bite into the wire. If those are removed, can the insulation be repaired with tape (vinyl or rubber) and stay compliant? If not, could he leave them in place and just disconnect the tap wires and be compliant?
    Click image for larger version.
Name:	Solar System Tap.jpg
  2. #2
    Join Date
    Dec 2012
    Placerville, CA, USA
    Posts
    19,941
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    Based on the diagram, the "panel B main breaker, which is not physically in panel B, is a service disconnect, with the main breaker in panel A also being a service disconnect. (Are they grouped?)
    That makes the PV connection a load side tap supplying the panel B bus but not located at the opposite end of the bus from the MB. Probably a violation, depending on the details of bus B rating, MB rating PV rating and sum of branch breakers.
  3. #3
    Join Date
    Apr 2007
    Berkeley, CA
    Posts
    1,795
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    That's a load side connection, so it doesn't match the approved drawings.
    Is panel B itself MLO? If so, then the NEC requires the feeder downstream of the PV tap, and the bus in panel B, to be rated at least the sum of the Panel B service disconnect breaker size and 125% of the inverter output current.
    Cheers, Wayne
  4. #4
    Join Date
    Apr 2007
    Huntington Beach, CA (19 Hrs. 22 Min. from Winged Horses)
    Posts
    6,871
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Coppersmith View Post
    cup-L-taps, or similar ilk, can be removed, and the damaged
    insulation repaired as any other nicked insulation would be.
    or i suspect you could leave them on, removing the tap, and
    just torquing them down. i'd remove them and use 2 layers of
    half lapped scotch 33, and move on.
    ~New signature under construction.~
    ~~~~Please excuse the mess.~~~~
  5. #5
    Join Date
    May 2011
    Posts
    4,864
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    A client of mine who is a solar contractor has installed the system depicted below. His approved drawing calls for a line side tap. The inspector says this is a supply side tap. It's on the line side of the panel but the [load] side of the MB. What is the correct answer?
    Terminology seems off the mark in your post. 'Line' and 'supply' are synonyms here. In the above quote I changed one instance of 'supply' to 'load' because that's what your diagram indeed shows (a tap on the load side of the MB, not the supply side]. In the other instances of 'supply' some clarification might be in order. What exactly did the inspector call which?
    In my opinion yes.
    I'd be a bit more concerned about exposed live parts inside those than conductor insulation repaired with tape. Still calls for tape around open holes, in my opinion.
  6. #6
    Join Date
    Jun 2016
    Tampa, FL, USA
    Posts
    2,008
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jaggedben View Post
    After a bit of research I agree. I was using the terminology the solar contractor told me. I also reviewed the drawing and found the engineer said "supply side" and showed a diagram where the taps are between the meter and the panel main. He doesn't show the separate main breaker before the panel.
    Quote Originally Posted by GoldDigger View Post
    Quote Originally Posted by wwhitney View Post
    So if we move the tap above the "service disconnect" (which would be right after the meter), does that make it line/supply side?
    (Are they grouped?)
    No they are not, but pre-exisiting so not an issue I hope.
  7. #7
    Join Date
    Oct 2009
    Austin, TX, USA
    Posts
    10,440
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Yes.
  8. #8
    Join Date
    Mar 2003
    Vermont
    Posts
    1,946
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Are these something useful?>>>
    ~RJ~
  9. #9
    Join Date
    Jan 2009
    3 Hr 2 Min from Winged Horses
    Posts
    15,961
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by romex jockey View Post
    ~RJ~
    What are they?
    "Electricity is really just organized lightning." George Carlin
    Derek
  10. #10
    Join Date
    Jun 2016
    Tampa, FL, USA
    Posts
    2,008
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jumper View Post
    What are they?
    They appear to be replacements for the tops of the lugs inside the meter can that allow the attachment of a tap conductor. I've never seen the tap done inside the meter can but I can't think of a reason you couldn't do it.