    Hello All,
    Installing 36 Sunpower AC modules. Each Module is rated at 1.33 Amps AC, 36 x 1.33 x 1.25= 59.85 Amps AC.
    We will be combining the module outputs into a combiner panel, which will itself have one output to feed the meter and main panel.
    Seeing as #6/3 NM is only rated to 55 amps, am I right coming to the conclusion that it cannot be used here, even though i am pretty certain that wire will never see 55 amps on it, due to losses and the fact that we oversize it for continuous use?
    Any thoughts on this?
    thanks
  2. #2
    Join Date
    Oct 2009
    Austin, TX, USA
    Posts
    10,891
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by JoeNorm View Post
    Hello All,
    thanks
    The amount of current you expect to see is irrelevant to the code; your design current is (36)(1.33A) = 47.9A. Your temp and conduit fill (if applicable) derated ampacity must be greater than that and (1.25)(47.9A) = 59.9A must be less than the 75 degree wire ampacity, assuming that you have 75 degree terminals. I don't know anything about the ampacity of #6/3 NM cable, though; what is the temperature rating?
  3. #3
    Join Date
    Jan 2009
    3 Hr 2 Min from Winged Horses
    Posts
    15,966
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ggunn View Post
    Temperature rating for NM-B is 90C for corrections/derating/adjustments but limited to a final ampacity of 60C per 334.80.
    "Electricity is really just organized lightning." George Carlin