Thread: Bonding Metallic Raceways Connected to Nonmetallic Equipment

  1. #1
    Join Date
    Feb 2005
    Location
    South of Bawstin
    Posts
    1,254

    Bonding Metallic Raceways Connected to Nonmetallic Equipment

    314.3 requires internal (Ex No.1) or integral bonding means (Ex No. 2) when metal raceways or metal-armored cables are used with nonmetallic boxes.

    Why is there no Code requirement for internal or integral bonding means for metal raceways or metal-armored cables used with nonmetallic equipment enclosures?

  2. #2
    Join Date
    May 2018
    Location
    Jamaica and london
    Posts
    967
    Even in a non metallic equipment enclosure isn’t there a bonding screw point or grounding screw point? If not, don’t you still treat it like a box, by tying grounds together, including using grounding bushings for metal conduits?
    Student of electrical codes. Please Take others advice first.

  3. #3
    Join Date
    Feb 2005
    Location
    South of Bawstin
    Posts
    1,254
    I don't see any requirement in the Code to bond the metal raceway or metal wiring method to the ground bar inside the nonmetallic equipment enclosure. 314.3 applies to boxes.

    I guess 250.4(A)(5) is the only section I can find that may apply. There would be lower impedance if the metal raceway or metallic wiring method was bonded at the nonmetallic equipment enclosure.