    We're tapping and extending from the secondary from these existing xfmrs so it's not imperative I figure it out, but I want to know why there's a 480/480 transformer. Is it because of distance (of which appears far diagrammatically via several hand holes). It doesn't appear they're using a neutral on the secondary side so not because they needed a wye... thoughts?
    eta for clarity, the question is: under what circumstance would you use a transformer of the same voltage and how would one size and specify?
  2. #2
    Join Date
    Feb 2003
    Seattle, WA
    Posts
    19,436
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    I have seen it used as a means of isolating the upstream and downstream distribution systems from each other. You size the transformer for the calculated load, just like for any other transformer. You specify a 1:1 turns ratio, and include whether the primary and secondary are to be connected WYE or DELTA.
    Charles E. Beck, P.E., Seattle
    Comments based on 2017 NEC unless otherwise noted.
  3. #3
    Join Date
    Jun 2003
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    10,741
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Would this be a method to reduce the available fault current?
    Tom
    TBLO
  4. #4
    Join Date
    Sep 2008
    UK
    Posts
    12,703
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ptonsparky View Post
    Could be. Chokes would be cheaper.
  5. #5
    Join Date
    Jul 2007
    Clark County, NV
    Posts
    2,027
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    If the xformer has a few taps for minor voltage differences, it could be used to account for voltage drop. It's nominally a 480/480, but might be hooked up to restore a 5% - 10% voltage drop.
    As mentioned, it could also be used as an isolation transformer.