    We're tapping and extending from the secondary from these existing xfmrs so it's not imperative I figure it out, but I want to know why there's a 480/480 transformer. Is it because of distance (of which appears far diagrammatically via several hand holes). It doesn't appear they're using a neutral on the secondary side so not because they needed a wye... thoughts?

    eta for clarity, the question is: under what circumstance would you use a transformer of the same voltage and how would one size and specify?

    Name:  Capture.jpg
Views: 224
Size:  8.2 KB
    Last edited by follybeacher; 10-26-18 at 03:39 PM.

  2. #2
    Join Date
    Feb 2003
    Location
    Seattle, WA
    Posts
    19,191
    I have seen it used as a means of isolating the upstream and downstream distribution systems from each other. You size the transformer for the calculated load, just like for any other transformer. You specify a 1:1 turns ratio, and include whether the primary and secondary are to be connected WYE or DELTA.
    Charles E. Beck, P.E., Seattle
    Comments based on 2017 NEC unless otherwise noted.

  3. #3
    Join Date
    Jun 2003
    Location
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    10,184
    Would this be a method to reduce the available fault current?
    Tom
    TBLO

  4. #4
    Join Date
    Sep 2008
    Location
    UK
    Posts
    12,147
    Quote Originally Posted by ptonsparky View Post
    Would this be a method to reduce the available fault current?
    Could be. Chokes would be cheaper.
    Si hoc legere scis nimium eruditionis habes.

  5. #5
    Join Date
    Jul 2007
    Location
    Clark County, NV
    Posts
    1,381
    If the xformer has a few taps for minor voltage differences, it could be used to account for voltage drop. It's nominally a 480/480, but might be hooked up to restore a 5% - 10% voltage drop.