    Grounding electrode & series string fuse

    Hi,

    We are building a carport structure for solar panels. I understand this falls under a "separate structure" for NEC grounding. I am thinking to use a 8ftx5/8" ground rod. My question is, do I need 2? Not following code on that easily.

    Next we are getting called by plan check for the listing of our panels calls out "series fuse rating 20A". As of right now we have SMA string inverters that do not have fuses for strings. Plan checker says it will violate warranty on panels if series string fuses are not installed. Any thoughts on this? He needs a letter from the panel manufacturer saying they are not needed and he has never been provided that.

    Thanks again!

  2. #2
    Join Date
    May 2011
    Posts
    4,701
    I think technically, unless you can prove that one rod has less than 25ohms resistance to earth, the code requires a second. A lot places I work don't enforce that, FWIW. I wouldn't bother with 5/8 as opposed to 1/2 myself. Another option would probably be to bury one of the steel structural members deep enough to qualify as an electrode.

    The plan checker is confused. See NEC 690.8 for whether any fusing is required (see exceptions). The series rating only applies to a fuse that's otherwise required. I'd ask him to show me the documentation that says otherwise.

  3. #3
    Join Date
    Sep 2012
    Location
    CA, US
    Posts
    132
    Okay, so I was reading the electrode section correctly with the 25 ohms to ground. Thanks.

    He is going off the module spec sheet in the electrical characteristics that has a line that says "series fuse rating 20A". Because it says that, he thinks its required to meet the listing of the module. And if we do not install one then it breaks the UL listing of the module and warranty of the module. Never heard that before and made me wonder. Is he still mistaken? I seem to think he is.

  4. #4
    Join Date
    May 2011
    Posts
    4,701
    Quote Originally Posted by electro7 View Post
    Okay, so I was reading the electrode section correctly with the 25 ohms to ground. Thanks.

    He is going off the module spec sheet in the electrical characteristics that has a line that says "series fuse rating 20A". Because it says that, he thinks its required to meet the listing of the module. And if we do not install one then it breaks the UL listing of the module and warranty of the module. Never heard that before and made me wonder. Is he still mistaken? I seem to think he is.
    Find the module installation manual and show him (presumably) that it doesn't require fuses in your situation. Here's an example I found for a well known manufacturer, hopefully yours says something similar. I would hope something along these lines would end the discussion.

    A maximum of two strings can be connected in
    parallel without the need to incorporate an overcurrent
    protection device (fuses, etc.) in series
    within each string. Three or more strings can be
    connected in parallel if an appropriate, certified
    over-current protection device is installed in series
    within each string.

  5. #5
    Join Date
    Oct 2009
    Location
    Austin, TX, USA
    Posts
    10,191
    Quote Originally Posted by electro7 View Post
    Okay, so I was reading the electrode section correctly with the 25 ohms to ground. Thanks.

    He is going off the module spec sheet in the electrical characteristics that has a line that says "series fuse rating 20A". Because it says that, he thinks its required to meet the listing of the module. And if we do not install one then it breaks the UL listing of the module and warranty of the module. Never heard that before and made me wonder. Is he still mistaken? I seem to think he is.
    Yes, he is mistaken as long as you are not combining more than two strings without fusing. Actually, the rule is a little different but it nearly always matches up to more than two strings needing fusing.

    It is a common misconception among inspectors who don't understand how solar works that conductors need to be protected from solar production, both on the AC and DC sides. Backfeeding, either from the service or from parallel wired strings is the only reason for OCPD. Solar components are current limited devices.

  6. #6
    Join Date
    Sep 2012
    Location
    CA, US
    Posts
    132
    Thanks!

    I am not finding any similar verbiage for Sunpower modules. Probably will need to add fuses. Going to try tech support though first.

    Thanks again!

  7. #7
    Join Date
    Oct 2009
    Location
    Austin, TX, USA
    Posts
    10,191
    Quote Originally Posted by electro7 View Post
    Thanks!

    I am not finding any similar verbiage for Sunpower modules. Probably will need to add fuses. Going to try tech support though first.

    Thanks again!
    SunPower DC modules are just like any other DC module in that respect; two strings max in parallel if there are no string fuses. SunPower AC modules are, well, AC, so this doesn't apply. SunPower AC modules are parallel AC with 12 modules max to a branch circuit.

  8. #8
    Join Date
    Sep 2012
    Location
    CA, US
    Posts
    132
    This plan checker is stuck on the Sunpower (DC module) spec sheet that says in the electrical characteristics "series fuse rating 20A". It doesn't even say required. He thinks that not having a fuse on each string will break the UL listing of the module and the warranty.

    How do I argue his point? I want to because this guy is pulling out all the stops and it is extra work for me to install separate fuses.

  9. #9
    Join Date
    Sep 2012
    Location
    CA, US
    Posts
    132
    I am planning no parallel combining, but instead taking each string to the inverter input terminals.

  10. #10
    Join Date
    Oct 2009
    Location
    Austin, TX, USA
    Posts
    10,191
    Quote Originally Posted by electro7 View Post
    This plan checker is stuck on the Sunpower (DC module) spec sheet that says in the electrical characteristics "series fuse rating 20A". It doesn't even say required. He thinks that not having a fuse on each string will break the UL listing of the module and the warranty.

    How do I argue his point? I want to because this guy is pulling out all the stops and it is extra work for me to install separate fuses.
    The guy is just plain wrong. Petty bureaucrats' only power is to say "no" and when they don't know their job it's frustrating. I feel your pain.

    I design a LOT of SunPower systems, both with AC and DC modules, and I have never run into anyone as ignorant as this guy is. Close, though. Does he have a supervisor who has a clue?

    I'd call or drop an email to SunPower tech support and get it in writing that their modules don't require a string fuse to keep their listing.