    I am connecting a photovoltaic system to a 3 phase load, and i am not clear with the criteria of sizing the neutral conductor of the inverter, the manufacturer manual does not say anything.
    As I undestood, if the voltages diferences between phases is less than 5%, there is not a problem to connect the neutral to the system, but i am not clear the size of the conuctor, i guess it should not be less than the grounding equipment conductor, but not how bigger it should be.
    I will appreciate your help with this doubt.
    Thanks,
  2. #2
    Join Date
    May 2011
    Posts
    4,864
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    The inverter manual will tell you if a neutral is required for your application. I believe that it's section 705.95 in the code that allows the neutral to be sized the same as the EGC if it's only used for measuring voltage and such. You may need a letter from the manufacturer to certify if it's that kind of neutral.
  3. #3
    Join Date
    Oct 2016
    Posts
    50
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jaggedben View Post
    Hi jaggedben,
    Thanks I am going to check, but the manual does not say nothing about the size of the conductor, for the grounding conductor yes, but not for the neutral.
    Regards,
  4. #4
    Join Date
    Jun 2004
    Cherry Valley NY, Seattle, WA
    Posts
    5,036
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    This post may be of interest. I think it boils down to what the manufacturer states about how the neutral is used. Perhaps you can contact them if the manual is silent?
    http://forums.mikeholt.com/showthread.php?t=188721
    Ethan Brush - East West Electric. NY, WA. MA
    "You can't generalize"
  5. #5
    Join Date
    Nov 2015
    CA, USA
    Posts
    715
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    You can't go wrong with a full-sized neutral.
    If you can tell from the manufacturer's documentation that the neutral is just used for measurement then you can downsize it to the same size as the EGC. Not all manufacturers will put this in their manual and you can't go by what some tech support person says on the phone, it has to be documented so you can show the AHJ if asked. If the AHJ is not convinced it can be expensive to have to rerun a full-sized neutral.
  6. #6
    Join Date
    Oct 2016
    Posts
    50
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by pv_n00b View Post
    Hi,
    The manual says about the neutral:
    "The inverter must be connected to a three-phase system with the center of the star connected to ground. To connect the inverter to the grid is possible to choose between the four-wire connection (3 phases + neutral) and the three-wire connection (3 phases)."
    But, I have a clue, they have indicate the same size of the glands of entrace of cables for the phases, maybe they are assuming that you are going to size the neutral with the same size of the phases.
    - Single-core configuration have 4xM40 cable glands for the “R”, “S”, “T” phases and for the “N” neutral cable and a M25 cable gland for the grounding cable.
    - Multi-core configuration (optional) have a M63 cable gland for the “R”, “S”, “T” phases and for the “N” neutral cable and a M25 cable gland for the grounding cable.
    i know, sounds stupid, it would be better if I await for the response from the manufacturer.
    Thanks to all, and regards.
  7. #7
    Join Date
    Oct 2009
    Austin, TX, USA
    Posts
    10,440
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by INGMRS View Post
    Hi,
    You have your answer. You can choose not to use a neutral. The three phases must be referenced to neutral/ground but you don't have to connect it.
  8. #8
    Join Date
    Jun 2004
    Posts
    5,036
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ggunn View Post
    I agree, but so bizarre....why do they even give an option? Why would someone spend time and money to run a neuter of its not required
  9. #9
    Join Date
    Oct 2009
    Austin, TX, USA
    Posts
    10,440
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by electrofelon View Post
    Nevertheless, it's a pretty common option in larger three phase inverters.
  10. #10
    Join Date
    Jun 2004
    Posts
    5,036
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    by larger do you mean central inverters?
    A few years ago, my friend told me about a situation with a solectria central inverter. He had already run wire I guess, and didnt run a neutral. Solectria told him how to set it up to run without a neutral, but implied it was "better" to use a neutral and to pull one next time. No one really seems to know definitively what the deal is with this neutral thing.