    Hi Everyone,
    I have an option to pull either 2/O CU or 300kcmil AL. Can anyone tell me in their experience, if the amount one saves on using aluminum is greater than the labor saved by pulling a smaller wire size on the copper?
    Thanks a lot
  2. #2
    Join Date
    Apr 2009
    Williamsburg, VA
    Posts
    6,042
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I would say in almost all cases with wires in those sizes that you will come out ahead with aluminum conductors, labor and materials both considered.
  3. #3
    Join Date
    Feb 2017
    NYC
    Posts
    14
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Thanks for your input!
  4. #4
    Join Date
    Jul 2003
    New Jersey
    Posts
    27,124
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    As for the installing either of the conductor types IMO it's a toss up. The real savings will be in the cost of the conductors but part of that may be eaten up if you need a larger raceway.
    Rob
  5. #5
    Join Date
    Apr 2003
    Fort Collins, Colorado
    Posts
    1,753
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by MGest View Post
    Hi Everyone,
    Thanks a lot
    Why 300 aluminum? 4/0 Al. is close to the ampacity of 2/0 cu.
    Ron
  6. #6
    Join Date
    Mar 2003
    New England
    Posts
    13,801
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    This is a no brainer, AL all day long. It's literally a fraction of the cost of copper.
  7. #7
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    40,565
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Important factor - how long of a run?
    Only 10 foot run, might still be less materials cost for aluminum but still be close enough you look at more at other advantages and not just cost.
    I live for today, I'm just a day behind.
  8. #8
    Join Date
    Dec 2012
    Placerville, CA, USA
    Posts
    20,169
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    It also depends on how the wire is going to be terminated. It is possible that some devices you plan to use are either not rated for Al or will not accept the wire size needed when using Al. Not a terribly likely situation, and can be accommodated using a pigtail, but still worth looking out for.
  9. #9
    Join Date
    Apr 2009
    Williamsburg, VA
    Posts
    6,042
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Good points by everybody here. Some of the exceptions where copper would be better is running to equipment that has lugs that can only accept copper conductors, having to go up to the next size raceway where the raceway is already installed or would be a giant pitb to upsize, where wire ampacities cross on the tables, and so on.
    Exceptions notwithstanding, generally you will come out way ahead with aluminum. Specifically, there are a few cases where copper is the only way to go, job spec being the number one reason.
    branch circuit wiring is almost exclusively run in copper, however that is why I mentioned in my first post regarding the wire sizes. You are almost never going to see number 12 in aluminum, 350 MCM is a different matter.
  10. #10
    Join Date
    Feb 2017
    NYC
    Posts
    14
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by rcarroll View Post
    thats what they're asking for. we gave them an VE alternative