250.66 - which if you learn how to use it properly you will see that it is based on the size of incoming conductors and has nothing to do with overcurrent device selection.Does anybody really have the dig on what the GEC to a waterline is based on?
You have a 500kcmil supply conductor - that is the basis whether you have a single 30 amp disconnect being supplied or 6 200 amp disconnects being supplied. (6 -200's is not impossible here - depends on load calculations)