User Tag List
Results 1 to 4 of 4
Thread: Question for the PV experts.
  1. #1
    Join Date
    Sep 2011
    woodbridge, ct. USA
    Posts
    1,168
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    If you have a 200 amp meter/main outside and a 200 MLO panel inside, can you tap the load side of the 200 amp breaker, outside in the meter main enclosure? I have been reading online and it appears to be a grey area.
    1. It's not really a supply side connection. NEC 705.12(A)
    2. If you put another main breaker in the MLO panel would that make it compliant. (assuming it is not compliant as is.)
    3. As is is there a possible over current issue?
  2. #2
    Join Date
    Nov 2015
    CA, USA
    Posts
    733
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    It's a load side interconnection and would have to go by 705.12(B)(2)(1) and that's going to require OCPD between the tap and the MLO panel, or a main CB in the panel.
  3. #3
    Join Date
    Oct 2009
    Austin, TX, USA
    Posts
    10,760
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by GerryB View Post
    It's not a supply side connection, it's a load side tap. If the MLO panel is rated than less than the service OCPD plus 125% of the maximum rated inverter output current, you must install a main breaker in the MLO panel. There also could be an issue with the feeder ampacity. Reference 2014 NEC 705.12(D)(2).
  4. #4
    Join Date
    Sep 2011
    woodbridge, ct. USA
    Posts
    1,168
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Thanks for those answers, very helpful.
Posting Permissions
  • You may not post replies