    Disconnect

    Doesn’t the 200 amp breaker in the panel
    satisfy this requirement?

    “230.70 General.
    Means shall be provided to disconnect
    all conductors in a building or other structure from the
    service entrance conductors”

  2. #2
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    4,818
    Quote Originally Posted by Fmkehoe View Post
    Doesn’t the 200 amp breaker in the panel
    satisfy this requirement?

    “230.70 General.
    Means shall be provided to disconnect
    all conductors in a building or other structure from the
    service entrance conductors”
    Yes. 99% of the time, the OCPD requirement, and the disconnecting means requirement are met with the same device.
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  3. #3
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    33,847
    Quote Originally Posted by Fmkehoe View Post
    Doesn’t the 200 amp breaker in the panel
    satisfy this requirement?

    “230.70 General.
    Means shall be provided to disconnect
    all conductors in a building or other structure from the
    service entrance conductors”
    Where is the 200 amp panel located?
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  4. #4
    Join Date
    Mar 2011
    Posts
    115
    If it's not located at the nearest point of entrance of the service conductors it would not. You would need a disco outside.