1/2 CONTROL RECEPTACLE

Status
Not open for further replies.

Toros

Senior Member
Location
Tujunga, CA
Hi,
Inspector walk in upon are request and checked the rough and every thing is all-right except 1/2 controlled outlets

we installed 2 cicuits in 4squre box one for reqular recept. and one for 1/2 control receptacle
inspector says that we can not have 2 circuits for difefrent plugs that all are in same box.

what is this?????
 

jumper

Senior Member
Hi,
Inspector walk in upon are request and checked the rough and every thing is all-right except 1/2 controlled outlets

we installed 2 cicuits in 4squre box one for reqular recept. and one for 1/2 control receptacle
inspector says that we can not have 2 circuits for difefrent plugs that all are in same box.

what is this?????

Inspector is incorrect.

Did inspector give a code reference?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Hi,
Inspector walk in upon are request and checked the rough and every thing is all-right except 1/2 controlled outlets

we installed 2 cicuits in 4squre box one for reqular recept. and one for 1/2 control receptacle
inspector says that we can not have 2 circuits for difefrent plugs that all are in same box.

what is this?????

What is this? Unless there's a pertinent detail missing it's nonsense. As others have stated ask for a code reference.
 

Sierrasparky

Senior Member
Location
USA
Occupation
Electrician ,contractor
What you did is perfectly acceptable,
My question is do you really need separate circuits. There is a potential that someone may get caught off guard by two circuits on a single strap and have some nice sparks.

However We can't always wire for the what if's
I would label the different circuits on the device on trim out.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
Hi,
Inspector walk in upon are request and checked the rough and every thing is all-right except 1/2 controlled outlets

we installed 2 cicuits in 4squre box one for reqular recept. and one for 1/2 control receptacle
inspector says that we can not have 2 circuits for difefrent plugs that all are in same box.

what is this?????

What the inspector should have said is IF you have 2 different circuits on the same yoke (same box) then you need to have either a 2-pole breaker on handle ties to turn both circuits off simultaneously.

Now if you just have two runs off the same circuit there is nothing restricting that.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
What the inspector should have said is IF you have 2 different circuits on the same yoke (same box) then you need to have either a 2-pole breaker on handle ties to turn both circuits off simultaneously.

Now if you just have two runs off the same circuit there is nothing restricting that.

Why would two circuits in the same box require simultaneous disconnect?
 

kwired

Electron manager
Location
NE Nebraska
Hi,
Inspector walk in upon are request and checked the rough and every thing is all-right except 1/2 controlled outlets

we installed 2 cicuits in 4squre box one for reqular recept. and one for 1/2 control receptacle
inspector says that we can not have 2 circuits for difefrent plugs that all are in same box.

what is this?????


Nothing wrong so far with what you have said, doesn't mean he isn't after something you haven't yet mentioned.

Start by asking for a code reference that is in violation then look at details as they relate to what has been cited.

One potential issue has been mentioned so far, two circuits on one yoke - could be a problem but there is a correct way to do that.
 
Status
Not open for further replies.
Top