Thread: Neutral sizing 220.61

  1. #1
    Join Date
    Jun 2011
    Posts
    20

    Neutral sizing 220.61

    220.61 states that the neutral load shall be the maximum unbalance of calculated between the neutral conductor and any one ungrounded conductor.

    If my panel voltage and capacity is 120/240VAC 400Amp load center and the loads connected are all 2 wire 240Volt appliances with balanced current on the 2 ungrounded conductors ex. electric heaters and water heaters what do I use to size my neutral to the panel?

  2. #2
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    33,847
    If this is a service then the neutral can be sized as small as the grounding electrode conductor. If it is a feeder then size the neutral no smaller than the equipment grounding conductor but if there are no neutral loads then you don't need a neutral for a feeder.
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  3. #3
    Join Date
    Jun 2011
    Posts
    20
    Quote Originally Posted by Dennis Alwon View Post
    If this is a service then the neutral can be sized as small as the grounding electrode conductor. If it is a feeder then size the neutral no smaller than the equipment grounding conductor but if there are no neutral loads then you don't need a neutral for a feeder.
    What article calls out the service neutral can be sized as small as the grounding electrode conductor? What article calls out the feeder neutral shall be no smaller than the equipment grounding conductor? I just want to read it and understand it.
    I do have a couple 20 amp lighting and receptacle loads on this panel so I know I have to at least size it to carry the load of them but it didn't seem right to size it so small and the ungrounded conductors to carry 400amps. What if someone in the future pulls out the balanced 240v loads and connects 120V loads?

  4. #4
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    33,847
    The 2017 has changed a bit so that Table 260.66 has been split up and now the grounded conductor is sized by the bonding jumper which is T. 250.102 which is basically the same as T250.66

    230.23(C) Grounded Conductors. The grounded conductor shall
    not be less than the minimum size as required by 250.24(C).
    (C) Grounded Conductor Brought to Service Equipment.
    Where an ac system operating at 1000 volts or less is grounded
    at any point, the grounded conductor(s) shall be routed with
    the ungrounded conductors to each service disconnecting
    means and shall be connected to each disconnecting means
    grounded conductor(s) terminal or bus. A main bonding
    jumper shall connect the grounded conductor(s) to each service
    disconnecting means enclosure. The grounded conductor(
    s) shall be installed in accordance with 250.24(C)(1)
    through 250.24(C)(4).


    (c)(1) Sizing for a Single Raceway or Cable. The grounded
    conductor shall not be smaller than specified in Table
    250.102(C)(1).
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  5. #5
    Join Date
    Apr 2009
    Location
    Williamsburg, VA
    Posts
    5,710
    Quote Originally Posted by darren12 View Post
    What if someone in the future pulls out the balanced 240v loads and connects 120V loads?
    In that case the neutral will carry the difference of the currents of leg A and leg B. For that to fry a typically downsized neutral, this would require the astronomically impossible odds of all 240-volt equipment being disconnected, and something like 20 1500 watt space heaters or 75 400w high pressure sodium lights to all be plugged in at once on just a single leg.

    Normally the 120 volt loads will be fairly balanced on each leg, which is required under 210.11(b), and also fairly low in many calculations compared to the 240 volt loads. if you had a perfect 50/50 split, there would be zero amps on the neutral... You would not even need a neutral under a perfect load split distribution.
    Electricians do it until it Hertz!

  6. #6
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    23,723
    Quote Originally Posted by JFletcher View Post
    You would not even need a neutral under a perfect load split distribution.
    That would be true only if there are no loads with a neutral at all. Balance can not be guaranteed otherwise.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  7. #7
    Join Date
    Jun 2011
    Posts
    20
    Quote Originally Posted by Dennis Alwon View Post
    The 2017 has changed a bit so that Table 260.66 has been split up and now the grounded conductor is sized by the bonding jumper which is T. 250.102 which is basically the same as T250.66



    (C) Grounded Conductor Brought to Service Equipment.
    Where an ac system operating at 1000 volts or less is grounded
    at any point, the grounded conductor(s) shall be routed with
    the ungrounded conductors to each service disconnecting
    means and shall be connected to each disconnecting means
    grounded conductor(s) terminal or bus. A main bonding
    jumper shall connect the grounded conductor(s) to each service
    disconnecting means enclosure. The grounded conductor(
    s) shall be installed in accordance with 250.24(C)(1)
    through 250.24(C)(4).


    (c)(1) Sizing for a Single Raceway or Cable. The grounded
    conductor shall not be smaller than specified in Table
    250.102(C)(1).

    I was looking at a feeder for a “sub panel” so I see that 215.2 (A) (2) says to use 250.122 and looking at 250.122 shows for a 400amp OPD use 3 AWG.

    Sound right??

  8. #8
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    33,847
    Quote Originally Posted by darren12 View Post
    I was looking at a feeder for a “sub panel” so I see that 215.2 (A) (2) says to use 250.122 and looking at 250.122 shows for a 400amp OPD use 3 AWG.

    Sound right??

    Yep--250.122 is the equipment grounding conductor. If there was a line to neutral short then the neutral would need to be sized the same as the equipment grounding conductor in order to safely trip the breaker. Imagine a long run with a #12 equipment grounding conductor, if there were a 100 amp breaker the chances are the #12 would not be capable of opening the breaker
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me