    Exam question

    Been stumped trying to locate the correct section to answer the following: Distance in inches between top of termination lugs to housing in a 100 A load center.

  2. #2
    Join Date
    Nov 2010
    Location
    Fort Collins, Colorado
    Posts
    2,748
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by chicagosparky View Post
    Been stumped trying to locate the correct section to answer the following: Distance in inches between top of termination lugs to housing in a 100 A load center.
    Seems to me you will need to make some assumptions as Table 312.6(B) goes by conductor size, not ampacity. Not sure it is a fair and valid question because depending on a number of factors the conductor size could vary for a 100 amp panel.

  3. #3
    Join Date
    Aug 2018
    Location
    Chicago, IL
    Posts
    25
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Thanks Texie, never thought of 312.6 B. That's gotta be it.