    Line-Side Interconnection on Building Disconnect Switch

    Hello,

    I want to interconnect a total of 150A of solar line side of a 400A building disconnect switch. The problem that I'm not sure of is what would be the best method/practice of interconnection. Not having much experience any advice is greatly appreciated. I attached a picture of the interconnection point for reference. Would it be best to see if I could replace the single set of lugs to double lugs or get a new disconnect switch with built-in 2 lugs per phase? Money isn't a factor here. Also, I would just need to keep a 400A disconnect switch frame since the solar offset the utility feed?

    Thanks again
    Attached Images Attached Images  

  2. #2
    Join Date
    May 2011
    Posts
    4,757
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Double lugs may be possible. Maybe insulation piercing connectors. The photo is a little bit too low resolution to get a good look. Looks like space is tight though.

    It wouldn't be a bad idea to discuss your plan with the AHJ before you do it.

  3. #3
    Join Date
    Aug 2004
    Location
    Irvine California
    Posts
    85
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I would change out disconnect using dual lugs . You will need the room pending on size of tap conductors


    Sent from my iPhone using Tapatalk Pro