    Panel fed from UPS a separately derived system?

    Is the load side of a UPS considered a separately derived system? i believe there is an isolation transformer in the UPS which would make me think it is. If i am feeding a load center from the UPS i should bond the neutral correct? most standby power i have worked with in the past has been generators so this is kind of new to me. thanks for any input!

  2. #2
    Join Date
    Feb 2003
    Location
    New York, 40.7514,-73.9925
    Posts
    4,604
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Generally if the UPS is a SDS, the N-G bond already occurred at the UPS output terminals.

    Newer UPSs are transformerless, and not SDSs. if it is the same voltage in and out.
    Ron