    Adding a ground bar to a 480 volt main distribution feeder panel.

    I want/need to add a ground bar to a 480 volt panel that is feed by a 600 amp main circuit breaker... What is the rule of thumb for adding ground bar to panels? Is there amperage requirements or standards to adhere to before installing a ground bar to this panel photos attattched

    Sent from my Moto Z (2) using Tapatalk

  2. #2
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    4,930
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Easiest thing is to get one from Siemens and it will come with the correct screws to go right into the existing holes. If I have to retrofit one, I will drill and tap 8-32 threads into the cabinet.
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  3. #3
    Join Date
    Dec 2006
    Location
    Eastern Oregon
    Posts
    3,655
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    We buy those Siemens panelboards all the time.

    Like Electro said, go to your siemens rep and ask for a ground bar or two for a panelboard, not a loadcenter. It'll be the type that comes wrapped in white paper, not in a clear plastic bag.

  4. #4
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    38,837
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I think OP might have concern over the current carrying ability of the bar being installed. My thought is if you put in a bar that only accepts 4 AWG maximum conductors in any port, it will have enough cross sectional area that it will carry anything a 4 AWG conductor can bring to it and the fact it is installed at a 600 amp panelboard means very little.

    If you need to terminate a larger conductor you will be getting a bar with larger ports - but to accommodate those that bar will physically be larger and will be able to handle any current the larger conductor can deliver to it.
    I live for today, I'm just a day behind.

  5. #5
    Join Date
    Dec 2011
    Location
    Ocala, Florida, USA
    Posts
    2,862
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by kwired View Post
    I think OP might have concern over the current carrying ability of the bar being installed. My thought is if you put in a bar that only accepts 4 AWG maximum conductors in any port, it will have enough cross sectional area that it will carry anything a 4 AWG conductor can bring to it and the fact it is installed at a 600 amp panelboard means very little.

    If you need to terminate a larger conductor you will be getting a bar with larger ports - but to accommodate those that bar will physically be larger and will be able to handle any current the larger conductor can deliver to it.

    My thought also.


    I know what I don't know, and I know where to go to find it!

  6. #6
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    4,930
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Even the bars that only have holes for #4 you can get those add on lugs that usually go up to 2/0 I think (thinking of square d stuff). I guess we are to assume that whatever fits is ok IIRC those siemens panelboard ground bars have many larger than #4 holes.
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  7. #7
    Join Date
    Dec 2006
    Location
    Eastern Oregon
    Posts
    3,655
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by kwired View Post
    I think OP might have concern over the current carrying ability of the bar being installed.
    Yep, I totally missed what he was asking. I read what I thought he said, rather than what he actually said.

    Quote Originally Posted by electrofelon View Post
    IIRC those siemens panelboard ground bars have many larger than #4 holes.
    You're right, there are several holes rated for 1/0 mixed in with the smaller ones.

  8. #8
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    38,837
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Cross sectional area of said ground bar isn't as critical as it is for a wire conductor, especially an insulated wire conductor that normally carries current.

    EGC may carry thousands of amps during a ground fault, but only has to do so for long enough time to clear the OCPD, and can take more temp rise than the insulation on a wire conductor on top of that, but at same time is short in length so you don't have the resistance you might have over many feet of a wire conductor either.
    I live for today, I'm just a day behind.