User Tag List

Results 1 to 2 of 2

Thread: ETAP Short Circuit Analysis Report Critical Error

  1. #1
    Join Date
    Nov 2017
    Location
    Philippines
    Posts
    7
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)

    ETAP Short Circuit Analysis Report Critical Error

    Hi Can anyone help me?
    I try to run Short Circuit Analysis and report shows the following critical errors.
    Please see my picture below.
    What could be the following solution?

    Name:  Short Circuit Analysis Report.jpg
Views: 97
Size:  59.5 KB

  2. #2
    Join Date
    Jul 2006
    Location
    SE USA as far as you can go
    Posts
    2,698
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    If you selected the breakers from the library, make sure you have selected the correct ratings. You can add additional devices if they are not in the built-in library.

    If the devices have been confirmed to be correct, then you need to look at your sources and make sure you have the energy input correctly. If that is all correct, then you have a breaker that is rated too low for the energy available.
    "Just because you're paranoid, doesn't mean they're not out to get you"