Thread: Would one get shocked by from hot case by pure Grounding Electrode Only?

  1. #11
    Join Date
    Mar 2003
    Location
    Vermont
    Posts
    1,892
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ptonsparky View Post
    We recently had a very similar situation where there was no grounded conductor or equipment ground at the equipment. Ground rod only. Measured voltage from rod to screwdriver stuck into the earth 6’ away was about 90 volts. Bolted fault to one of the phases.

    Yes, you get shocked.
    I'm guessing a delta ....~RJ~

  2. #12
    Join Date
    Jun 2003
    Location
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    10,303
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by romex jockey View Post
    I'm guessing a delta ....~RJ~
    No, it was 120/240 single phase. No EG was run with the 240 v lighting circuits to poles.
    Tom
    TBLO

  3. #13
    Join Date
    Nov 2018
    Location
    new york
    Posts
    145
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)


    The voltage gradient in the soil above assumes the street light pole metal enclosure and ground rod is same location. But how about if the metal enclosure (like panel enclosure below) and ground rod distance differs. Where will you draw the gradient circles below.. in the center of the ground rod or the panel case? I'd like to understand what gradients (just qualitatively) the person feet are exposed to.


  4. #14
    Join Date
    Jun 2003
    Location
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    10,303
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by tersh View Post


    The voltage gradient in the soil above assumes the street light pole metal enclosure and ground rod is same location. But how about if the metal enclosure (like panel enclosure below) and ground rod distance differs. Where will you draw the gradient circles below.. in the center of the ground rod or the panel case? I'd like to understand what gradients (just qualitatively) the person feet are exposed to.

    Using the gradients in the upper picture, how far away from the ground rod is your stick figure?

    The gradient will will be different at your house than mine. It most likely will be different than the guy with two rods versus your one. Dry sand vs wet clay?

    Is is he standing on concrete in direct contact with the soil or does it have two inches of insulation under it as mine does?
    Tom
    TBLO

  5. #15
    Join Date
    Nov 2018
    Location
    new york
    Posts
    145
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ptonsparky View Post
    Using the gradients in the upper picture, how far away from the ground rod is your stick figure?

    The gradient will will be different at your house than mine. It most likely will be different than the guy with two rods versus your one. Dry sand vs wet clay?

    Is is he standing on concrete in direct contact with the soil or does it have two inches of insulation under it as mine does?
    The person is say 10 meters away (32 feet) from local electrode ground rod (the panel is also 10 meters away from ground rod). Let's assume the person stands on bare feet and dry sand. So I guess the gradient concentric circle starts at the local electrode ground rod (you can make it two rods.. I just want to know where to start the gradients circle and if the person would be shocked)?

  6. #16
    Join Date
    Jun 2003
    Location
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    10,303
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by tersh View Post
    The person is say 10 meters away (32 feet) from local electrode ground rod (the panel is also 10 meters away from ground rod). Let's assume the person stands on bare feet and dry sand. So I guess the gradient concentric circle starts at the local electrode ground rod (you can make it two rods.. I just want to know where to start the gradients circle and if the person would be shocked)?
    I’ve never done the testing so keep that in mind. IMO. The gradients shown in the illustrations are not static. They will change from day to day and possibly hour to hour. Totally dry sand may not allow enough current to flow, while working your feet down three inches could be an eye opener. Being shocked is also subjective.

    We can’t tell you that at exactly 32 feet you will feel a shock or how strong you judge it to be. Do you run Marathons in your bare feet or haven’t had your shoes off outside in 30 years. How old are you? Male, Female? IDK what transgender will do to that.
    Tom
    TBLO

  7. #17
    Join Date
    Oct 2007
    Location
    New Jersey
    Posts
    6,264
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by tersh View Post
    The person is say 10 meters away (32 feet) from local electrode ground rod (the panel is also 10 meters away from ground rod). Let's assume the person stands on bare feet and dry sand. So I guess the gradient concentric circle starts at the local electrode ground rod (you can make it two rods.. I just want to know where to start the gradients circle and if the person would be shocked)?
    1. At the ground rod.
    2. Since you mentioned "bare feet", probably, keeping in mind all the caveats ptonsparky mentioned.

  8. #18
    Join Date
    Feb 2003
    Location
    Illinois
    Posts
    23,850
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    The gradients stay pretty much the same. They are based on percentages of the total soil resistance, and assume that 100% of the voltage is dropped within x' of the grounding electrode. I think most such tables assume 100% drop at 25-50 feet from the rod. All a lower soil resistivity does is increase the current from into the earth. The voltage drop at x' remains relatively constant for various soil sensitivities.
    Don, Illinois
    (All code citations are 2017 unless otherwise noted)

  9. #19
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    38,837
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by tersh View Post


    The voltage gradient in the soil above assumes the street light pole metal enclosure and ground rod is same location. But how about if the metal enclosure (like panel enclosure below) and ground rod distance differs. Where will you draw the gradient circles below.. in the center of the ground rod or the panel case? I'd like to understand what gradients (just qualitatively) the person feet are exposed to.

    Panel and rod are at same potential because there is a bond conductor between them, disregarding any voltage drop on that bond conductor which will be negligible anyway if it is short length, so that leaves you with how far are you from the rod where you are contacting earth will determine what voltage you are subjected to. If the panel were mounted on a conductive/semi conductive surface, there may be additional voltage gradient zones present relative to that surface.
    I live for today, I'm just a day behind.

  10. #20
    Join Date
    Aug 2018
    Location
    Virginia
    Posts
    95
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by tersh View Post

    What does NEC and other codes say about this, and theoretical considerations?

    In a nutshell, the NEC requires a low impedance path back to source to trip the OCPD.