    Quote Originally Posted by TheElectrician View Post
    Yes this is underground, But the Power Company code book says the following:

    "Three-phase secondary cables shall be phase grouped in the case ofconcrete ducts and HDPE conduits ( Phase A, B,C and neutral in thesame conduits) and shall be phase isolated in the case of steel conduits(Phase A, B,C and neutral in separate conduits)."

    Let me know your thoughts
    If you do that with ferrous raceways, there will be heating effects on the raceways, and higher overall impedance in your conductors. You want one of each phase and neutral where used in each raceway so that their opposing magnetic fields cancel one another and has less heating issues on the ferrous raceway.

    Brass, stainless, aluminum or non metallic conduits aren't a problem - they are non magnetic.
    I live for today, I'm just a day behind.

  2. #22
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    4,930
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by tkb View Post
    Why is your neutral full size for solar?
    The code is such that the inverter needs to state that the neutral is for voltage reference only. Some do and some dont. I have actually never seen a reduced neutral, even though most of the systems I have,seen and worked on use inverters that state the neutral is for reference only. Its a rediculous waste IMO.
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  3. #23
    Join Date
    Nov 2015
    Location
    CA, USA
    Posts
    706
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by TheElectrician View Post
    Thanks everyone for your information. It was really helpful. Since I am running 6 sets of A,B,C and N and using Steel Conduit, my Power Company requires the conductors to be phase isolated in the case of steel conduits(Phase A, B,C and neutral in separate conduits). So I am running 4 conduits.

    Utilities do not have to comply with the NEC. If these conductors fall under utility control then you follow their rules, if they fall under the NEC then you follow the NEC. If the utility wants to apply utility rules to NEC systems then you have a problem.

  4. #24
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    34,006
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    Utility rule or not I would not do it. I have a engineer friend who had a huge issue with this in Durham, NC... He was called in to see what the trouble was and it didn't take long before he saw the problem. The conduits were incredibly hot which was causing problems with the terminals, etc.
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  5. #25
    Join Date
    Dec 2018
    Location
    New York, NY, USA
    Posts
    12
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by TheElectrician View Post
    Thanks man, I will confirm with them again
    Yes, I was actually researching about it, also kwired gave some insights on post#21. I would like to get your point of view also if you dont mind.

  6. #26
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    34,006
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    I don't know if anyone has posted the section but here it is.

    300.3(B)(1) Paralleled Installations. Conductors shall be permitted tobe run in parallel in accordance with the provisions of
    310.10(H). The requirement to run all circuit conductors
    within the same raceway, auxiliary gutter, cable tray, trench,
    cable, or cord shall apply separately to each portion of the
    paralleled installation, and the equipment grounding conductors
    shall comply with the provisions of 250.122. Parallel runs
    in cable tray shall comply with the provisions of 392.20(C).


    Exception: Conductors installed in nonmetallic raceways run underground
    shall be permitted to be arranged as isolated phase, neutral,
    and grounded conductor installations. The raceways shall be installed
    in close proximity, and the isolated phase, neutral, and grounded
    conductors shall comply with the provisions of 300.20(B).
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  7. #27
    Join Date
    Aug 2018
    Location
    Chicago, IL
    Posts
    28
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    What's the length of the run? If it is under 100 feet, then no big deal. but if it's longer than 100', trying to pull 7 or 9 conductors in one raceway becomes "troublesome".

  8. #28
    Join Date
    Dec 2018
    Location
    New York, NY, USA
    Posts
    12
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Dennis Alwon View Post
    I don't know if anyone has posted the section but here it is.
    Thanks for posting this

  9. #29
    Join Date
    Dec 2018
    Location
    New York, NY, USA
    Posts
    12
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by chicagosparky View Post
    What's the length of the run? If it is under 100 feet, then no big deal. but if it's longer than 100', trying to pull 7 or 9 conductors in one raceway becomes "troublesome".
    the run is certainly less than 100'

  10. #30
    Join Date
    Dec 2018
    Location
    New York, NY, USA
    Posts
    12
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by LarryFine View Post
    Do you understand what's wrong with separating phases in metallic conduit, so you can voice your objection?
    Yes, I was actually researching about it, also kwired gave some insights on post#21. I also found a few topics related to this which was useful:

    http://forums.mikeholt.com/showthread.php?t=122170&highlight=magnetic

    http://forums.mikeholt.com/showthrea...light=magnetic