    200 3 Phase Service Question

    I am taking on a side job where as of right now there is a 200 Amp Meter outside. It comes through the brick wall in conduit and up through an LB right into the main panel. The new owners of the building want to move the panel around 45 feet down the wall. Can I just install a 200 Amp Enclosed Breaker where the current panel is and then just run conduit in the work space and go to a new 200 Amp Main Breaker (SUB) Panel? Nothing in the NEC says I have to have that main service disconnect outside right? The main service disconnect would be about 3-4 feet inside the building.

  2. #2
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    23,901
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Putting a new main where the M/B panel is now should be okay. Don't forget that you will need a four-wire feeder from the new main to the newly-relocated panel, the neutrals and grounds must be separated, and the existing panel's bonding screw or jumper removed.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  3. #3
    Join Date
    Feb 2003
    Location
    Bremerton, Washington
    Posts
    8,008
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Keep in mind the distance you can run "unfused" service entrance conductors may be subject to local rules. In Washington, we allow up to 15 ft of raceway, and restrict the raceway to 8 wiring methods (no EMT).
    Moderator-Washington State
    Ancora Imparo

  4. #4
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    23,901
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Tom, he said enclosed breaker, which is also what I meant by main, and 3 to 4 feet.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA