    Table 314.16A (Box fill)

    In the box fill table, it lists the basic 2-1/2" deep metal switch box as only being able to hold 6 #14 conductors (or 5 #12). How would these even be of any use if that precludes a typical installation of 2 #14 romex cables and a switch (such as for a light)? That in itself would be 7 conductors (4 current carrying, 1 ground, and 2 for the device). Not to mention an additional one if the kind with the internal clamps is used. Am I missing something here?

  2. #2
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    33,973
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    They are good for dead end not feed thru. When we have to use metal we use the 3 1/2" deep boxes
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  3. #3
    Join Date
    Nov 2007
    Location
    Livonia, Michigan
    Posts
    360
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Dennis Alwon View Post
    They are good for dead end not feed thru. When we have to use metal we use the 3 1/2" deep boxes
    Oh I see. I never noticed this until just now. I hardly ever use metal boxes unless I need to install one within a return-air stud cavity. I guess I need to use 4" square ones with device rings.

  4. #4
    Join Date
    Nov 2007
    Location
    Livonia, Michigan
    Posts
    360
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Were the box fill requirements different in the 1960's? Because nearly all the homes in my subdivision have the same size metal nail-on boxes, even with feed-thru outlets, whether #12 or #14 is used. So I never gave it a second thought until now.

  5. #5
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    26,334
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    You use that box with only one cable or you'll need a deeper one.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted