    Open neutral

    I disconnected the neutral from a sub panel without flipping the breaker off. Shouldn’t all those sub panel circuits be dead. Tv, wireless router, microwave clock still indicated power. Water heater gas valve control now dead and also gave off a burned electrical smell. Refrigerator not working properly. Power block for cable modem dead. Clock radio turned on by itself, now dead. Anyone venture an idea of what happened? And yes I know I’m an idiot and shouldn’t be anywhere near a main panel much less a light switch.

  2. #2
    Join Date
    Jul 2005
    Location
    Tennessee
    Posts
    16,018
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    A reply as a courtesy prior to closing the thread:

    Disconnecting the neutral on a 240/120 circuit places all 120v loads in series creating unstable voltages as shown in this sketch.
    Name:  open neutral.jpg
Views: 98
Size:  18.9 KB
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.

  3. #3
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    19,856
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    I am closing this thread, in accordance with the Forum rules. This Forum is intended to assist professional electricians, inspectors, engineers, and other members of the electrical industry in the performance of their job-related tasks. However, if you are not an electrician or an electrical contractor, then we are not permitted to help you perform your own electrical installation work.


    If I have misjudged the situation, if for example this project is related to your work, then send me a Private Message. If you can show me that I am wrong, and that you are a licensed electrician (or at least a licensed apprentice), then I will reopen your post, and offer an apology for the delay and inconvenience.

    A reminder to all members, if you see a questionable post, feel free to report it by clicking the button at the bottom left corner of the post.
    -------

    That said, I will also point out to you that the various loads connected to L1 and L2 form a voltage divider across the 240V potential, with the open neutral bus being the connection between the two sides. The result is that, depending on the resistance of the things connected to both legs the voltage across each side can range from close to zero volts all the way up to close to 240V. You are fortunate the results were not worse.
    PS: What Augie said....