Pole Lights and Ground Rods

Status
Not open for further replies.

tom baker

First Chief Moderator
Staff member
And the appropriate reference is article 250.32(A). It starts by saying each separate structure (and a light pole counts as being a structure) shall have a grounding electrode system.


I don't have my electronic version of the NEC available, but there is an exception that lighting poles are not considered structures, otherwise we would have to install disconnects at each one.
 

iwire

Moderator
Staff member
Location
Massachusetts
I don't have my electronic version of the NEC available, but there is an exception that lighting poles are not considered structures, otherwise we would have to install disconnects at each one.

Tom, that is not correct.

Poles remain structures, the exception is directly to the requirement requiring a disconnect. It does not change the GES requirements.

225.32 Location. The disconnecting means shall be installed
either inside or outside of the building or structure
served or where the conductors pass through the building or
structure. The disconnecting means shall be at a readily
accessible location nearest the point of entrance of the conductors.

For the purposes of this section, the requirements
in 230.6 shall be utilized.

Exception No. 1: For installations under single management,
where documented safe switching procedures are established
and maintained for disconnection, and where the
installation is monitored by qualified individuals, the disconnecting
means shall be permitted to be located elsewhere
on the premises.

Exception No. 2: For buildings or other structures qualifying
under the provisions of Article 685, the disconnecting
means shall be permitted to be located elsewhere on the
premises.

Exception No. 3: For towers or poles used as lighting
standards, the disconnecting means shall be permitted to be
located elsewhere on the premises.

Exception No. 4: For poles or similar structures used only
for support of signs installed in accordance with Article
600, the disconnecting means shall be permitted to be located
elsewhere on the premises.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
In this whole thread I don't believe anyone has mentioned that if the pole itself is metal and goes 10ft in the ground, it can be its own electrode and definitely no ground rod is required.

I certainly agree that if the pole meets the requirements then adding a ground rod will do zilch.

Lightning protection is a whole other code.
 

kwired

Electron manager
Location
NE Nebraska
In this whole thread I don't believe anyone has mentioned that if the pole itself is metal and goes 10ft in the ground, it can be its own electrode and definitely no ground rod is required.

I certainly agree that if the pole meets the requirements then adding a ground rod will do zilch.

Lightning protection is a whole other code.
But they are typically attached to a concrete base. Said base may not quite qualify (per NEC) to be a CEE, but many still believe what is there is likely a better electrode in majority of cases then a typical 8 foot ground rod is.
 

kwired

Electron manager
Location
NE Nebraska
And the appropriate reference is article 250.32(A). It starts by saying each separate structure (and a light pole counts as being a structure) shall have a grounding electrode system. It then gives an exception that says you don't need a grounding electrode system if the structure (light pole) is fed from a single circuit (including, if appropriate, a multi-wire branch circuit) that includes an equipment grounding conductor. That is why Bob's statement about more than one branch circuit or a feeder is correct.


I don't have my electronic version of the NEC available, but there is an exception that lighting poles are not considered structures, otherwise we would have to install disconnects at each one.

Unless the pole light is supplied by more than one branch circuit, or a feeder the NEC does not require a grounding electrode at the pole.

First two quotes were comments following the last quote here.

There is also the exception following 250.32(A) that fits into this conversation if the light pole is only supplied by a branch circuit:

Exception: A grounding electrode shall not be required where only a single branch circuit, including a multiwire branch circuit, supplies the building or structure and the branch circuit includes an equipment grounding conductor for grounding the normally non—current-carrying metal parts of equipment.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
But they are typically attached to a concrete base. Said base may not quite qualify (per NEC) to be a CEE, but many still believe what is there is likely a better electrode in majority of cases then a typical 8 foot ground rod is.

As long as the pole goes 10ft into the ground, it's an electrode. Concrete doesn't matter. Code says 'with our without concrete encasement'. 250.52(A)(2)(1).

I suppose in many cases it may be cheaper and require less logistical organization to just drive a rod than to increase your digging depth to 10ft for the pole base, or to build bases with CEEs in them. I was just sayin' what the code allows.
 

jumper

Senior Member
As long as the pole goes 10ft into the ground, it's an electrode. Concrete doesn't matter. Code says 'with our without concrete encasement'. 250.52(A)(2)(1).

I suppose in many cases it may be cheaper and require less logistical organization to just drive a rod than to increase your digging depth to 10ft for the pole base, or to build bases with CEEs in them. I was just sayin' what the code allows.

Isn't this rather a moot point since a GE is not required?
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Maybe a regional thing, here everything gets a concrete base. Likely due to winter.
Another reason, for poles on or near a vehicular path, is to provide a breakaway joint to reduce injury when the pole is hit. Without it the pole can either come down very hard on top of the car or cause a major incursion into the front.
 

iwire

Moderator
Staff member
Location
Massachusetts
Another reason, for poles on or near a vehicular path, is to provide a breakaway joint to reduce injury when the pole is hit. Without it the pole can either come down very hard on top of the car or cause a major incursion into the front.

Maybe but we install many conreate bases at grade level.
 

tom baker

First Chief Moderator
Staff member
Tom, that is not correct.

Poles remain structures, the exception is directly to the requirement requiring a disconnect. It does not change the GES requirements.
The intent of this exception, thanks for finding it, was to clarify that a disconnect is not required at each pole, I have seen pictures of poles with fused discos on each one
 

kwired

Electron manager
Location
NE Nebraska
As long as the pole goes 10ft into the ground, it's an electrode. Concrete doesn't matter. Code says 'with our without concrete encasement'. 250.52(A)(2)(1).

I suppose in many cases it may be cheaper and require less logistical organization to just drive a rod than to increase your digging depth to 10ft for the pole base, or to build bases with CEEs in them. I was just sayin' what the code allows.

The pole usually isn't in the ground though, just connected to some anchor bolts embedded in the base. There is often rebar in the base but I don't know that it typically would qualify as a NEC recognized CEE, but I still believe in many cases will have less resistance to earth then a ground rod.
 

iwire

Moderator
Staff member
Location
Massachusetts
Not in California. There is a limit to the height above ground of the concrete base.
Direct buried wood posts have horizontal holes bored near the base to create a weak spot.

So no standard telephone poles?

In thinking of this some more, some of the cites and towns near me do use direct burred concrete poles for street lights. Just have never seen direct buried metal ones in this area.

Here if the lighting pole is out in the open of a parking lot we will use a raised base, however if it is in an island or outside the curbs along the edges it will often be down at, or a few inches above grade.
 