334.15

Status
Not open for further replies.

dnem

Senior Member
Location
Ohio
Old
334.15
(B) Protection from Physical Damage
[note: second paragraph]
Type NMC cable installed in shallow chases or grooves in masonry, concrete, or adobe, shall be protected in accordance with the requirements in 300.4(E) and covered with plaster, adobe, or similar finish.

New/Revision proposal
334.15
(B) Protection from Physical Damage
[note: second paragraph]
Type NMC cable installed in shallow chases or grooves in masonry, concrete, or adobe, shall be protected in accordance with the requirements in 300.4(F) and covered with plaster, adobe, or similar finish.

Substantiation: . When 330.4 was amended for the 2008 code cycle, this reference was not properly updated.
 

ryan_618

Senior Member
David: Nice catch. You could probably just email Jeff Sargant at NFPA and have him fix it though, if you don't want to go through the code change process.

BTW: Have you looked to see if this is an errata item that has already been caught?
 

dnem

Senior Member
Location
Ohio
ryan_618 said:
BTW: Have you looked to see if this is an errata item that has already been caught?

No, would it be easier to just send it in with my other proposals and let them sort it out ?
 